Fuse and Cable

02/04/2012 5:37 AM

If we want to provide fuse to an induction motor which is battery operated through VFD , should the protection be concerned to Overloaded protection or short circuit protection. I know both are similar conditions,differing in current situations only , but i want to know it for designing time delay fuse, such as,

For short or grnd fault protection it can be rated wrt the "calculated motor FLC "

ie. ( 150% FLC)

For overload protection it can rated wrt the " motor name late rating".

ie. ( 150% FLA) ( 150% according to NEC 430.32 for dc circuits).

Another question, Shouldnt the fuse Amp rating be equal to or less than the cable ampacity? (As per NEC 430.15 current rating of cable is 125% of FLC ).

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Fuse and Cable

02/04/2012 10:44 AM

VFD implies it is a 3 phase AC motor then right? If that's the case, then the VFD (if it was made any time in the last 10 years) is protecting the motor for both short circuit and overload, you don't need anything on the output side of the VFD. So all you need to do it protect the line side of the VFD.

Since you are obviously in the US, you are required to size the circuit conductors (and therefore the OCPD) feeding the VFD at NO LESS than 125% of the max amp draw of the VFD, regardless of the motor connected to it (430.22 I think). The VFD data sheet would tell you the max amp draw, and for a VFD they are always referring to the DC bus anyway, so the value would apply here. You don't need for them to be time delay fuses, and in fact most VFD manufacturers will tell you to use high speed "semiconductor" fuses. If you do that though, size them to the maximum allowed by code, usually 250% of the VFD rating.

But also double check your voltage issues. Many people forget that the DC voltage needed for a VFD is a lot higher than the AC voltage, because you lose the RMS effect in charging the DC bus. So if you are feeding a 480V rated VFD, the DC voltage you need to give it will be 678VDC, which then moves you out of "low voltage" as far as wiring and such. If it is a 240V drive, you need to feed it with 340VDC minimum, so from a wire insulation standpoint 600V rated wire is fine, but from a fuse standpoint, fuses come either as 170VDC class or 500V class and above, you will need to use 500V class fuses.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
2
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#2

Re: Fuse and Cable

02/05/2012 5:16 AM

Do not use a fuse between VFD and motor, the s/c, e/f and o/l protection should be provided by VFD as described in another post and rupturing may damage the VFD anyhow. The VFD should also include output phase loss protection and often you can interface a motor thermistor or thermocouple if you are very concerned re the motor running state. if you have multiple motors this is different again so maybe you should offer more information if this is your concern for individual protection.

If you mean the fuse to an induction motor on the supply side (by DC), you will select the cable and fuse protection according the the voltage and current level as you would with AC, following local regulations. Is this a rescue battery or marine application and what voltage is it? Also, what is the load when you are using battery power?

Naturally, for all VFD's, a faster fuse is preferred but not always used because of cost, size and availability but unless it's a fatigue failure, it often may be decided by the size of VFD and the relative difference in damage and danger the two rupture characteristics offer. If it's a small VFD inside a steel enclosure, for example, many do not choose faster fuses.

BTW, AC rectified to DC is the same voltage level peak to peak, so no difference here but I guess this is not relevant as this is battery anyway.

__________________
Something new every day!
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Aug 2011
Posts: 93
#3

Re: Fuse and Cable

02/06/2012 12:40 AM

Battery voltage is 48Vdc going to vfd.

VFD rating is 375 - 500A ( 2min RMS) 48VDC.

My motor full load current is 178A ( FLC-design current) , 160A ( name plate FLA).

I m trying to provide a dual time delay fuse at the battery side.

So should the fuse rating depends on motor name plate reading or design FLC?

If so should the fuse rating be lesser than cable ampacity( 125% of FLC)?

And am i right with the fuse protection given for short circuit and overload in the first post? If not please correct me.........

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Fuse and Cable

02/06/2012 3:50 AM

The overload setting is there to protect the motor.

The fuses are there to protect the wiring.

British Standard 7671 and evermore shall be so.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Aug 2011
Posts: 93
#5

Re: Fuse and Cable

02/06/2012 7:15 AM

i have two VFDs of: 1) 375A/20.8KVA (2 min RMS) and

2) 500A/27KVA ( 2min RMS).

If my induction motor FLA is 180A, then from the above two VFDs which one will be most suitable? Sorry the efficiencies are not mentioned, i need to know for deciding

1)the input fuses rating and

2)input /output cable ampacities.

Please suggest yours fuse and cable ratings. Thank you.....

Register to Reply
Commentator

Join Date: Aug 2011
Posts: 93
#6

Re: Fuse and Cable

02/08/2012 1:52 AM

I should have asked this question first before going further detailed that,

How do we size fuses and cables for VFD?

Is it wrt to Motor FLA or VFD current rating? I m confused because in NEC 430.122 it has mentioned about both.

I m asking these questions because i m new to mthis job in practical and i dont want to make mistakes..........

Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#7
In reply to #6

Re: Fuse and Cable

02/08/2012 3:01 PM

I would start with the drive manufacturer's specifications.

For the drives that we commonly use, AB Powerflex drives, the user guide published by AB has a table of the maximum recommended fuses, type and size, and also a set of recommendations for cable types and sizes.

I believe that, for the reasons that have been given by other posters, it is prudent to size the feeder protection and cables to the drive to the rating of the drive, even if it is intended to only part-load the drive with a smaller motor. Any less, and all it takes is for someone to replace the small motor with one that fully loads the drive without up-ratinging the feeder cabling, and you have a situation that is ripe for a meltdown.

__________________
paulusgnome
Register to Reply
Commentator

Join Date: Aug 2011
Posts: 93
#8

Re: Fuse and Cable

02/09/2012 7:34 AM

I have a question which is running through my mind, and is mostly concerened with the input fuses for inverter. Is an inverter just like a transformer? ie the inverter consumes current from the battery depending on inverter rated value and delivers the output depending on motor load value by suitable switching configuration for constant V/hz value?

or

Does the inverter consumes current from the battery depending on motor load? If so which shouldn't we size the fuse according to motor FLA ?

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JRaef (1); MalcolmK (1); Paulusgnome (1); PWSlack (1); sujinvipin (4)