Earthing

02/28/2012 5:33 AM

Why in low voltage,grounding solidly earthed while in MV it is resistance earthed ?

also in HV,what type of earthing we use and why ?

Register to Reply
Pathfinder Tags: earthing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#1

Re: Earthing

02/28/2012 6:08 AM

Life is not so simple. Earthing systems in LV and MV differ from country to country, and is linked to habits, regulations, and sometimes the type of usage (i e IT neutral management in hospitals).

You will find a complete course in electrical installation design on :

http://www.electrical-installation.org/enwiki/Electrical_installation_design_methodology

Register to Reply Score 1 for Good Answer
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#2

Re: Earthing

02/28/2012 7:15 AM

Another interesting link to a debate about pros and cons of IT systems in LV

http://engineering.electrical-equipment.org/forum/general-discussion/it-earthing-system-for-or-against

Register to Reply Score 1 for Good Answer
3
Associate

Join Date: Jan 2010
Posts: 25
Good Answers: 1
#3

Re: Earthing

02/28/2012 8:27 AM

Earthing has nothing to do with system voltage. When you connect the neutral of a star connection to earth. It is called system earthing. It can be solid earthing, resistance or reactance earthing.

It is provided for various reasons like

a) elimination of arcing grounds.

b) voltage on healthy phase during earth fault on one of the phases will not rise above phase voltage. hence equipment connected to other phases are safe.

c) earth fault protection scheme becomes easy and simple.

Type of earthing depends on

a) fault level of the system.

b) Rotating machines on Secondary side of Transformer.

c) Earth Fault protection scheme.

Register to Reply Good Answer (Score 3)
4
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#4

Re: Earthing

02/28/2012 9:55 AM

Why... quite simple really. A MV system can deliver more energy into a fault. So, by using a resistance in the ground path back to the source, we limit the possible current flow to a level that is only high enough to ensure the operation of the overcurrent devices. This limits the energy dumped into a fault.

By limiting the fault current levels we minimize equipment damage caused during a fault event and reduce the cost of installation by allowing for systems less hardened to withstand the effects of high fault currents.

For lower voltage system that can generally deliver far less fault current into a fault, these precautions are seldom needed.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 4)
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

North of 60 (1); obouill (2); S SRINIVASAN (1)

Previous in Forum: Isochronous Mode and Droop Mode   Next in Forum: Cable Sizing

Advertisement