Dry Type Transformer Failure

02/28/2012 8:53 AM

I have a 50kVA dry type transformer which had failed, with rating:

1. Input (LV, primary winding): 400V, 72.17A
2. Output (HV, secondary winding): 21.5kV, 1.34A

3. Average Output usage (single phase, DC): 24kV, 1.35A


The failed area was found to be the HV winding, where arcing and sign of localized overheating was observed . Calculations showed no overload to input or output. Observation of the other similar and unaffected transformer also showed same overheated marks on the upper portion of the HV winding.

What would have cause the overheating? probable cause of the failure?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Dry Type Transformer Failure

02/28/2012 9:57 AM

OK. I'll start. I'm guessing a >+10% voltage excursion event on the primary winding.

Is there a prize for getting this right, BTW?

__________________
Good moaning!
Register to Reply
Participant

Join Date: Feb 2012
Posts: 2
#2
In reply to #1

Re: Dry Type Transformer Failure

02/28/2012 10:05 AM

Good morning.

How do you get the >10% voltage on the LV primary side?

My calculation: P=EIx1.73; E=400V, I=58A

Thus, input power about 40kVA, less than normal rating 50kVA.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#3
In reply to #2

Re: Dry Type Transformer Failure

02/28/2012 10:18 AM

I don't get a >+10% voltage on my windings. I don't know anything about your power source so any surge in voltage will be on your equipment.

__________________
Good moaning!
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#5
In reply to #2

Re: Dry Type Transformer Failure

02/28/2012 11:36 AM

It's funny how transients happen so damned fast!!!

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Dry Type Transformer Failure

02/28/2012 11:11 AM

From past experience dirt springs to mind. What sets of as a slight leakage soon builds up until flashover occurs giving you the burning you see now.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6

Re: Dry Type Transformer Failure

02/28/2012 1:00 PM

Probable cause of the failure?

Voltage spike damaging inter-turn windings of HV coil resulting in eventual (not necessarily instant) arc/overheating and damage to HV winding within a localised part of the transformer.

Could also be a transformer manufacturing defect (or a combination of the two).

__________________
jack of all trades
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#7

Re: Dry Type Transformer Failure

02/29/2012 1:45 AM

Your records showed no sign of any overload so that is not the cause

What would have cause the overheating? ...Inadequate cooling most likely if the above is really true.

The failure is the result of a process culminating in an event. Step by step and your other trafo looks like it is on the way out too.

Look carefully at the environment. Do you trust the manufacturer's rating claims? Did some one omit a derating factor at the onset?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Active Contributor

Join Date: Feb 2012
Location: Norfolk, England
Posts: 11
#8

Re: Dry Type Transformer Failure

02/29/2012 2:12 AM

Have your checked the inrush (start-up) current for the equipment being powered. We recently have found that some of the equipment installed on our site has higher inrush currents than specified by the manufacturer of the equipment. If the inrush is higher than the transformer rating this could be what's caused your problem. With our problem the inrush was found to be approx 4 times the nominal rating of the transformer and at present we are lucky that it has not burnt out.

Register to Reply
Participant

Join Date: Feb 2012
Posts: 2
#9

Re: Dry Type Transformer Failure

02/29/2012 9:35 AM

It sounds more of a lightning strike, than over load, and the taps on the primary side...

Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#10

Re: Dry Type Transformer Failure

02/29/2012 10:53 AM

The most common cause of failure on dry type HV transformers are insulation break downs on the magnet wire and inter-winding insulation. Deterioration of conformal coatings triggered by the combined accumulation of dirt and moisture. Heating is the after effect when HV arcing starts to develop due to the deterioration of this insulation.

__________________
vsar
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#11

Re: Dry Type Transformer Failure

03/02/2012 3:37 AM

Failure may be due to following reasons:

You have mentioned,' Average Output usage ( single phase, DC ) : 24kV, 1.35 A. That means the output AC voltage is converted to DC voltage for some special application( not mentioned ). If IGBTs are used for DC conversion, high volatge pulses may hit the HV windings and in effect interturn failure of HV windings may be happened. Due to interturn failure , localised heating may be occured and ultimately insulation may be damaged and trafo may be failed.

If there are harmomics in load side and fed to trafo, loaclised heating and failure of insulation may occur.

If the condition of epoxy insulation are not good,i.e.,there are pores/ air pockets in epoxy insulations, partial discharge at high voltage may occur and inturn localised heating and failure of epoxy insulations.

If photographs are available and nature of load or application in details are availabe, analysis of failure will be easier.

Thanks,

Manindra.

__________________
Manindra
Register to Reply
Participant

Join Date: Feb 2012
Posts: 1
#12

Re: Dry Type Transformer Failure

03/05/2012 5:27 AM

This is a rectifier Transformer application the failure may be attributed to the high dv/dt causing the damage to the start of the winding.
The actual reasons of the failure can only be commented after seeing the failure and kind of insulation scheme used for the transformer.

1.The class of insulation on the conductors?
2. During the design what was the stress level on the insulation?
3. What are the harmonics level Consideration during the design?

4. Background of Application?

I have got these questions from our technical manager, if you answer those, we can help you more. You may write to *

Regards,

Sujit

DuPont Nomex Team

*CR4 Admin - email address removed

From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers and email addresses posted in threads or comments. You can share this information via the CR4 internal messaging system.

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#13

Re: Dry Type Transformer Failure

03/05/2012 11:53 PM

My opinion is failure was caused by corona. (partial discharge)

The overheating was caused by a partial short where the corona ate through the insulation.

If when you disassemble the coil, the insulation is eaten away in other areas of the coil, this is a sure indication that there was corona in the coil.