Voltage transformer back energization

02/28/2012 2:04 PM

Is there is any technical issues if i back energize a Voltage transformer?

I have a gas insulated VT with rated primary voltage 115KV and sec voltage 115V.What is the significance of doing Vt back energization test?

__________________
"Miles to go before I sleep"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Voltage transformer back energization

02/28/2012 4:25 PM

What type of transformer has a 115KV primary and a 115 volt secondary? Watch you dont manage to kill yourself or anyone else.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4
In reply to #1

Re: Voltage transformer back energization

02/29/2012 3:40 PM

An instrument transformer (either VT or CCVT) used for transmission level relaying & metering could be of that ratio. They're usually connected phase-to-ground. They are not high capacity (maybe 500 to several thousand VA), but they do have that high a ratio. You can get them even higher, such as 345kV or 500kV primary.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5
In reply to #4

Re: Voltage transformer back energization

03/01/2012 5:38 PM

Agreed... but, someone who would work with this class of equipment on a regular basis would not likely be asking for advice in this forum.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Member

Join Date: Sep 2011
Location: Riyadh
Posts: 9
#7
In reply to #1

Re: Voltage transformer back energization

03/05/2012 7:56 AM

Hi

Just search about the components in a HV substation.....

__________________
"Miles to go before I sleep"
Register to Reply
3
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: Voltage transformer back energization

02/28/2012 6:57 PM

So long as you realise the HV voltage is lethal, and you do not exceed LV winding rated current or voltage [use a VARIAC 115V source, LV ammeter and LV voltmeter and step slowly up from zero volts], I do not see any issues for the transfo.

But you must be very sure the LV and HV winding are grounded and YOU are not the shortest, most inviting, path to ground from the HV terminal.

Personally, I would like to be behind a tall grounded metal mesh fence, standing on metal sheet, all bonded to the transfo LV winding ground, turning the variac from the far end of a wooden broom handle. Heavy duty voltage dependent resistors across the LV winding would be a good precaution.

These things are best done with all the right gear and precautions, according to an approved written procedure from the manufacturer, whose warranty probably depends on following that.

This would at least show the HV winding will take rated voltage. It should be possible to compare the LV magnetizing current with the specified HV magnetising current X transfo ratio.

Register to Reply Good Answer (Score 3)
Member

Join Date: Sep 2011
Location: Riyadh
Posts: 9
#6
In reply to #2

Re: Voltage transformer back energization

03/05/2012 7:54 AM

Thanks for your reply...

Above said VT is installed in gas insulated substation (GIS).This VT has 2 secondary cores (115V & 155/1.73V).Our plan is to inject voltage in one secondary core and measure Im and voltage induced in other secondary core.Nothing is going to measure in primary.Thanks for the precautions mentioned in your reply.I already contact the manufacturer for their comments.

__________________
"Miles to go before I sleep"
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8
In reply to #6

Re: Voltage transformer back energization

03/06/2012 5:27 AM

Thank you for clarifying the installation.

If you had mentioned two facts, at the expense of a minute on the keyboard by you....

  1. The V.T. is installed in switchgear.
  2. It has two secondaries.

-- the concerns of CR4 folk about safety would have been allayed and the possibilities for test more evident.

I hope you have learnt the importance of including all the relevant facts in a question.

67model

Register to Reply
Member

Join Date: Sep 2011
Location: Riyadh
Posts: 9
#9
In reply to #8

Re: Voltage transformer back energization

03/06/2012 12:40 PM

Yes Boss,,,,,,,,, will be specific next time,,,,,, thank you.....

__________________
"Miles to go before I sleep"
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Voltage transformer back energization

02/28/2012 9:59 PM

I've got to ask, why are you wanting to do these tests? Have you got the equipment to measure the OP voltage if you do the tests?

Pure folly to my mind.

Blow yourself up if you want, please don't endanger anyone else!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (2); finasks (3); North of 60 (2); PeterT (1); TonyS (1)

Previous in Forum: DVR Faulty   Next in Forum: Busduct

Advertisement