Busduct

02/28/2012 2:19 PM

Hi, I'm working now in a high rise building project and the electrical engineer is specifying a vertical busduct to distribute power in floors. As you know all floor penetrations must be plugged with a fire stop to hold smoke and fire to propagate to the upper floors. But in case of a fire the metal of the busduct also gets heated and would tramsmit this to the floors and would impose a risk. How do you prevent this? Isolating the duct every x floors with a switch? Apprecciate you comments.

Register to Reply
Pathfinder Tags: Busduct fire rotection
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#1

Re: busduct

02/28/2012 2:45 PM

A fire barrier (provided by Bus Duct manufacturer) is placed where the duct travels between floors. They are rated in hours, and will be selected based on the Fire Code for your area.

Is this a perfect solution? Absolutely not. However we have not learned to design buildings that will not burn.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply Good Answer (Score 4)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Busduct

02/28/2012 3:41 PM

Each bus duct mfr will have their floor / wall penetrantion systems only listed for fire ratings using a specific Fire Stop seal material, so it's crucial that you read and follow their instructions. A lot of people get burned by that (no pun intended).

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Busduct

02/28/2012 10:09 PM

I've got to ask, are you qualified to undertake this sort of work?

To ask the question it wouldn't seem so.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4
In reply to #3

Re: Busduct

02/29/2012 2:09 AM

We all encounter first time problems to surmount.

OP did the right thing and asked. This will set him/her on the right track.

OP, as previously recommended talk to your busduct supplier to get their complete penetration solution.

OP will learn that vendors are an excellent source of free consultation and will put their nads on the line for a sale. Just get it all in writing.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2008
Posts: 18
#7
In reply to #4

Re: Busduct

02/29/2012 8:42 AM

Dear threaders, I have posed the question to suppliers and am awaiting their reply. It seems to me (for the replies sent) that I did not set forth my question in a clear manner. The problem is not in the firestop (that is solved already); the problem is in the heating of the metal bar (current carrying) inside the busduct, that will transmit the heat from a fire up and "might" ignite something in the above floors if there's the threat. As you all know heat is one of the legs of the fire triangle.

Regards

Register to Reply
2
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#9
In reply to #7

Re: Busduct

02/29/2012 4:55 PM

Dear aguilafede,

Perhaps my reply was not clear enough. The fire stop that is provided by the manufacturer of the bus duct for installation between floors is your only remedy. If that system fails, another floor becomes involved and perhaps the building is lost.

Installing a switch in your system to provide discontinuance during a fire will work if the method is UL Listed (or whatever listing agency has authority where you work) and is approved by the bus duct manufacturer. I know of no such approved system. Would a similar system be employed for the potable water and drainage pipes to mitigate thermal creep?

Incidentally, there is no such thing as a fire triangle. Many years ago it was discovered that a fourth component was required for fire to exist; the reaction of the other three. What we not have is a fire tetrahedron.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#5

Re: Busduct

02/29/2012 2:27 AM

You may try fire resistant busducts of compact and sandwitch design where fire stops are not needed. These are housed within a galvanised steel housing or extruded aluminium housing with epoxy compound powder coating.

Register to Reply
Participant

Join Date: Apr 2010
Posts: 2
#6

Re: Busduct

02/29/2012 4:29 AM

Most fire stop materials supplier have their fire stop design for busduct through penetration.

e.g. 3M and Hilti.

The fire stop design is not dependent of busduct manufacturer. You can use the design as long as the busduct is correct type and size.

Actually, there is no such fire resistant busduct in the world as there is no such recognized standard for busduct. Some manufacturers used some fire resistant tests for cable to cheat consultants and their customers. But the tests are actually not applicable to busduct, otherwises, you will find IEC issued related standard or test requirement.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Feb 2012
Posts: 2
#8

Re: Busduct

02/29/2012 9:46 AM

Don't understand your question....what do you mean by isolating the bus duct x floors with a switch?

Register to Reply
Active Contributor

Join Date: Nov 2008
Posts: 18
#10
In reply to #8

Re: Busduct

03/01/2012 9:00 AM

Thanks for replying. I think the question was answered clearly by WFMFIRE, heat will be transmitted also by steel water piping, HVAC ducts and other. So what remains to be done is to firestop all between floors penetrations.

Regards

Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

aguilafede (2); debata07 (1); Gersh (1); JRaef (1); SkywalkerHK (1); TonyS (1); Wal (1); WJMFIRE (2)