Previous in Forum: Question on How to Calculate Depth of Thread for UNF   Next in Forum: Selection of Value of X-Capacitors that are Used in Differential Mode Filters
Close
Close
Close
6 comments
Rate Comments: Nested
Active Contributor

Join Date: Feb 2009
Posts: 15

Electrical Generators

02/28/2012 7:37 PM

Could any one help me, how can i evaluate how many electrical generators will be recomendable to install in order to have a power plant whic will output 80 Kw.

Thanks in advance for your contribution.

Best regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Electrical Generators

02/28/2012 7:57 PM

Synchronizing generators is not a good idea for a novice. Just buy one 80 kwatts generator.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Electrical Generators

02/29/2012 1:13 PM

Get just one, then you don't need to worry about syncing multiple generators to get all the phases to match, balancing load currents between generators, etc.

Commercially available generators go up to about 2MVA so one that will do around 80kW shouldn't be a problem.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#3

Re: Electrical Generators

03/01/2012 1:33 AM

One generator operating at around 75-80% load is fine.

Around 100kVA would work.

This is a simplistic answer of course. You may have some special operating conditions that need to be considered.....

Is this for prime or standby duty? If it is prime what redundancy do you need?

What is the service application? How do you know that your loading is 80kW?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Feb 2012
Location: Norfolk, England
Posts: 11
#4

Re: Electrical Generators

03/01/2012 2:01 AM

As Wal indicated there is other information required here in order to give a more suitable answer to your query. There is also the type of load, what voltage do you wish to operate (80kw - possibly 400V), does it need to synchronise with the mains, what payback period do you want? If you are unsure what you require, you would be better asking a company that specialises in generator supplies to investigate and offer a solution that is specific to your site.

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#5

Re: Electrical Generators

03/01/2012 4:26 AM

Normally generators are rated in kVA not kW. Assuming a reasonable power factor go for at least 100kVA. Computer loads are very bad loads so take care. Likewise you must consider the largest drive you have on the plant. A DOL motor has a large start up current and should be no more than 25% the rating of the generator to ensure a start.

If you are connecting to existing plant you will need to consider the Zs of the generator which might be too high to clear your protection.

Register to Reply
Guru

Join Date: Jun 2006
Posts: 501
Good Answers: 8
#6

Re: Electrical Generators

03/01/2012 7:18 AM

One. You can rent (buy) gen sets of 1/2 mega watt. Aggreco, GE. Do a web search.i

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dvalnrd (1); jack of all trades (1); jmart23 (1); redfred (1); silverfox (1); Wal (1)

Previous in Forum: Question on How to Calculate Depth of Thread for UNF   Next in Forum: Selection of Value of X-Capacitors that are Used in Differential Mode Filters

Advertisement