Anonymous Poster #1

Selection of Breaker for APFCR panel

02/29/2012 1:16 AM

Hello every one,

In one of my Commercial project I have selected Transformer of 1750 KVA as per the load, for that i have selected 625 KVAR APFCR panel, for this panel i have selected 1200 Amps ACB as main incommer of panel.

I calculated based upon this formula

Breaker= ((output KVAR * 1000)/ ((supply vltg)*sqrt(3)))*1.5

and by thumb rule: kvar x 2 = 1250 Amps

My conclusion is Whether this calculation is correct? and what is the difference between ACCP panel and APFCR panel ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Selection of Breaker for APFCR panel

02/29/2012 9:37 AM

Automatic Power Factor Correction Panel, APFC Panels, Switch ...

If you ever find APFCR panel, let us know.

Reply
Active Contributor

Join Date: Oct 2011
Posts: 20
#2
In reply to #1

Re: Selection of Breaker for APFCR panel

02/29/2012 11:52 PM

What is the difference between ACCP and APFCR panel? where it is used ?

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Selection of Breaker for APFCR panel

03/01/2012 7:19 AM
Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#4

Re: Selection of Breaker for APFCR panel

03/02/2012 8:46 PM

Friend,

I have not done this, but have two thoughts. First, the manufacturer of the APFCR and its panel would normally specify the size of overcurrent protection they require. Second, it seems to me that a load requiring 625 kVAR for power factor correction on a transformer rated at 1750 kVA is rather heavy on the kVAR rating. Perhaps I am wrong, but that is my "gut feeling". -JMM

Reply
Reply to Forum Thread 4 comments
Copy to Clipboard

Users who posted comments:

jmueller (1); lyn (2); mannsyed (1)

Previous in Forum: Selection of Cables, Fuses, SFU & Breaker for Motors   Next in Forum: BDV Value

Advertisement