Brushless AC-Motor Controller

02/29/2012 7:37 AM

Dear All,Referring to the subject above, i have the PCB which are responsible to control Brush less AC Motor.As you seen below it's gate driver circuit/Power circuit consist of IGBTs burnt completely and my job is to find out the cause of this incidents which occur most of the times.I have perform some working but still i did not come to conclusion why this happening all the time.My observation are listed below:Since the prime objective of this PCB is to control the speed and movement of the motor so i have make sure that there is no mechanical hindrances are their which leads towards this accident.Secondly.. the Input of this PCB is corresponds to R,S,T i.e. three phase so i have cross check the voltages and i have got some readings which are listed below:

Phase to Phase (380Volts)

Brown

Grey

Black

384 389 392
384 390 388
392 385 389
385 388 387
392 384 389
393 385 388
386 390 387
378 377 381
386 390 388
376 375 380
386 388 389
396 394 395
382 385 387
395 394 394
382 386 387
380 381 381
379 380 378
379 381 380
378 377 378
381 380 381
380 380 381

UNQUOTE:-------------------------------------------------
Therefore we need suggestions at any end why this happening and what are the reasons behind this...
Favorable reply needed in this regards,
Best Regards,
AND,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Nov 2007
Location: A secret. Bats are a Protected Species.
Posts: 186
Good Answers: 4
#1

Re: Brushless AC-Motor Controller

02/29/2012 8:46 AM

Oh, dear. That looks a bit horrible.

__________________
Innuendo is not Italian for a suppository.
Register to Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Brushless AC-Motor Controller

02/29/2012 9:24 AM

Just taking a wild guess I would guess that you have an improper sizing of driver to motor and load. This can be from a defective driver, a counterfeit driver, a poor understanding of the stored mechanical energy or even just a poor design of the driver module. You need to do a proper forensic failure analysis of your design. This cannot be done quickly and certainly not over a free blog. There is one thing that I don't see that bothers me. I see that you have thermal compound on what appears to be a diode bridge. I do not see any compound on those six smoked power transistors. It appears that no provision for cooling these transistors were made in your design.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Associate

Join Date: Apr 2007
Posts: 50
#3
In reply to #2

Re: Brushless AC-Motor Controller

02/29/2012 9:59 AM

If you take a close look on smoke IGBT picture you will find a heat larger heat sink exactly equal to the size of the whole PCB and unfortunately i didnot take the complete picture to show you completely...

Secondly... i did not agreed with your guess, i try to explain in more practical way...

I have use this type of controller in our machines which produced socks, and we have divide all the machines catogrically like LINE A,B,C,D,E,F and each lines consist of 25 Machines that is equal to 25 controllers (PCB) each IRT-Drive is responsible to control one machine and all the requirements like "Improper sizing of driver to motor or load" temperature issues, defective driver will cover from the manufacturer and done properly i.e. upto the requirement of the machine.

What we notice is that LINE A and LINE B has a good reputation in respect of accidents means the ratio of these type of occurence is much much lesser as compare to LINE C,D,E,F keep in view that all the parameters like machine capacity, model, power, voltage rating and load are similar...

what i show to you is the INPUT side in terms of voltage readings (describe in first post) because we have find only difference in each lines which leads to this sort of casualty is phase to phase minor voltage varaition but how i can practically prove that this is because of this voltage varaiation if that is the case.. OR you guys help me to work out how i solve this problem...

Iam available to provide any information you want to know about this sort of problem...

Help out...

Register to Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4
In reply to #3

Re: Brushless AC-Motor Controller

02/29/2012 10:32 AM

I don't care how large the heat sink happens to be, I do not see any heat sink compound on those transistors. So there appears to be no effective thermal contact area to cool these transistors. I also notice that there is no obvious method to use the mounting holes in the transistors to secure them to a heat sink. So I told you my conclusion from what I saw.

If you're going to dismiss my observations and opinions then I ask you why did you come here? It seems to me that you do not take others ideas very well. You seem to already have an unstated opinion what caused your driver to fail. You may have an infant mortality problem, you may have had a power surge at your facility that went through this driver. I do not know this and I do not care. This is not my facility, its yours. A real full blown forensic analysis of a system failure requires access and knowledge of the whole system and operating conditions. I can only analyze the data and images you present. Dismissing my observations just wastes both of our time.

Good Bye.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
2
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#5

Re: Brushless AC-Motor Controller

02/29/2012 11:12 AM

Failure reasons of this kind of beasts can be overvoltage from line spikes or regen-braking a high inertia load (plus possibly deteriorated bulk capacitors), drain overcurrent, current shoot through, faulty logic and/or overcurrent protection, gate destruction due to high Vge, faulty gate driver(s), too big or too small gate resistors, Severely unmatched IGBTs, load shorts, IGBT aging due to working near it's limits, blah, blah, take a pick. Unless you do some serious parameter (and waveform) monitoring at working conditions (not only voltage), all you can do is speculate. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply Good Answer (Score 2)
Associate

Join Date: Apr 2007
Posts: 50
#8
In reply to #5

Re: Brushless AC-Motor Controller

02/29/2012 11:59 PM

Dear Sir, a very productive and observable reply received at your end, with reference to your feedback i think two things are much similar as what i observed.

1) Over Voltage from line spikes

2) Drain over current

lets talk about point-1 that how we observe or analyse or detect Over Voltage from line spikes...

and how we measure drain over current...

Thanks in advance...

waiting for your favorable reply...

Register to Reply
Power-User

Join Date: May 2007
Location: Hurst, Texas
Posts: 178
Good Answers: 4
#10
In reply to #8

Re: Brushless AC-Motor Controller

03/01/2012 3:50 AM

Put good low pass emi filtering on supply and find mov or similar device to go across the supply phases. Find out what the nominal voltage of phases to ground. Use properly sized mov or vdr to snub the spikes.

Are the lines sourced to a central supply separately or taken from one line to another.

Does the "a" line supply and other subsequent lines daisy chain each line.(not a good technique.)

Separate each line and use emi and mov's on each line/machine.

I can cite many instances of dirty power causing these kind of issues.

Remove any added on accessory devices and run the on separate power source.

Are other devices hooked into the power for these machines or feed back to the same source?

__________________
Bill H.
Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#16
In reply to #8

Re: Brushless AC-Motor Controller

03/01/2012 5:33 PM

Now let's get to specifics. From the photo you provided I think I can see a circuit deficiency. The W output is directly connected to output and a "turn" does not pass through a core like Y and V, which I must assume is for current feedback to the controller. On normal conditions this scheme is OK since the third branch carries the algebric sum of the other two currents, but this is not the case for shooot-through current (in W branch) or if for some reason W suffers a short with power rails. By pure coincidence, W driving IGBT pair has given the biggest bang, and the high side IGBT the worst. This is also consistent with a W short to (-) but I would investigate the shoot through scenario first. Can you give the gate driver types and gate resistor values? (both low and high sides) S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Associate

Join Date: Apr 2007
Posts: 50
#17
In reply to #16

Re: Brushless AC-Motor Controller

03/02/2012 12:20 AM
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6

Re: Brushless AC-Motor Controller

02/29/2012 5:26 PM

What are the motor and drive ratings? How many amps was the motor drawing?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Apr 2007
Posts: 50
#7
In reply to #6

Re: Brushless AC-Motor Controller

02/29/2012 11:53 PM

Dear Sir,

Motor ratings are listed Below:

RCV Turin Italy

Lyra 28

Nm30-Kw1.25-w42-V202-A4.5

and Driver Rating (R,S,T)=220V

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9

Re: Brushless AC-Motor Controller

03/01/2012 2:00 AM

Your voltage readings in the table were all around 385, yet the motor and controller are rated at 202 and 220 volts. Was the motor accidentally wired in delta versus star?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Apr 2007
Posts: 50
#11
In reply to #9

Re: Brushless AC-Motor Controller

03/01/2012 4:45 AM

Sir the voltage readings i have shown you it basically came out from five stages..

1) Output from Generation Unit (400V)

2) Becomes input to the Distribution Side (400V)

3) Then Distribution Output will become the input of the Voltage Stabilizers of each lines (A,B,C,D,E and F)

4) Finally the output of the Voltage Stabilizer will become the Input (380V which fetch as input of the machine Transformer) of each machines which are connect to this stabilizer.

5) and Hence the output of Transformer i.e. 230V will become the Input of Drive (R,S,T)

Register to Reply
Commentator

Join Date: Dec 2009
Posts: 87
Good Answers: 5
#12

Re: Brushless AC-Motor Controller

03/01/2012 6:12 AM

Ok, the input voltage is for sure not the issue.

To give you good explanations from remote is close to impossible -From the photo it is hard to judge what happened. But I think I can notice "shoot out craters" close to the right pins of the upper two IGBTs. This the area where the bond wires between chip and pin where molten and exploded due to the exessive heat. This is a sever damage and happens when a lot of current can flow

VFD need in most cases special fuses super fast blowing in the supply line - to prevent such damage - are they in place and have you checked withthe supplier of the VFD?

Have you checked that the rating of the motor and and VFD fit each other and the VFD control unit is not overloaded . Especially consider instant high load changes on the motor

Consider possible shorts in the supply cables to the Motor due to movement of the cables or irregular current follow due to damage of the cables.

other reason i could imagine that the isolation between the IGBT and the heatsink is not vibration resistant and after some time will cause a short. It would be interesting to see the burn marks on the Heatsink side.

Discuss the burns withthe vendor of the VFD or the maschine it was build into.

Best regards

Register to Reply Score 1 for Good Answer
Associate

Join Date: Apr 2007
Posts: 50
#13
In reply to #12

Re: Brushless AC-Motor Controller

03/01/2012 7:42 AM

Sir here is the image of heat sink for better understanding....

Register to Reply
Commentator

Join Date: Dec 2009
Posts: 87
Good Answers: 5
#14
In reply to #13

Re: Brushless AC-Motor Controller

03/01/2012 10:55 AM

Thanks for the picture. I see that there is heatsink grease and persumably also heat conducting rubber plate below the transistors.I understand that the cabinet is alo used as a heat sink, So clearly the shoot through goes also through the rubber foil - that is might be an indication that the material does not withstand the voltage levels which occure inside the circuit.

And annother issue makes me wonder. Clearly to the left of the left transistor group there are two spots where a direct break through from the PCB! to the heatsink sheet metal is visible. I suspect that the PCB has not enough stand off to the heatsink and you get arking there. The area of the left transistor group looks pretty sotfree.

Naturally also an exploding capacitor can be the reason. But I would check for the standoff issue at first.

Difficult to give a hint but I would try to really find out what material the original manufacturer is using - the material is widly used but there different materials which look the same but have different properties. In a PC where most of the stuff is used you find only low voltages 3.3V - but here you need material with 1KV standing power at least. There are power electronic grade materials out there.

Ok what is happening is a severe disaster but the severe burns I would not expect. Can it be that ol and fibers cause the severe burning?

Could it be that by accident someting can press the heatsink sheet metal in direction to the PCB and create some shorts on the board?

What is the purpose of the two threaded parts blow the the transistors?

Sorry not to be able to give you a good hint regarding the issues at hand.

Best regards

Register to Reply
Associate

Join Date: Apr 2007
Posts: 50
#18
In reply to #14

Re: Brushless AC-Motor Controller

03/02/2012 12:40 AM

Thanks for your keen consideration... i am responding in bold to your comments.

Thanks for the picture. I see that there is heatsink grease and persumably also heat conducting rubber plate below the transistors.I understand that the cabinet is alo used as a heat sink, So clearly the shoot through goes also through the rubber foil - that is might be an indication that the material does not withstand the voltage levels which occure inside the circuit.

Since this sort of incidents occuring instantly so i observed that sometimes on some DRIVES heat found little greasy and sometimes on some DRIVES heat sink found lush shinny... so i think black smokes are very much common in all the cases of incidents.

And annother issue makes me wonder. Clearly to the left of the left transistor group there are two spots where a direct break through from the PCB! to the heatsink sheet metal is visible. I suspect that the PCB has not enough stand off to the heatsink and you get arking there. The area of the left transistor group looks pretty sotfree.

Naturally also an exploding capacitor can be the reason. But I would check for the standoff issue at first.

With this sort of incidents only GATE DRIVER CIRCUIT are mostly damage and during repairing i only focus on the gate driver section and none of any case i have found any CAPACITOR has been found exploded.

Ok what is happening is a severe disaster but the severe burns I would not expect. Can it be that ol and fibers cause the severe burning?

It is true that these drives are install in the area where fly waste (yarn) are present since the panels are close properly but still after several weeks i have perform preventive overhauling so it might be possible fly waste are helping to burn more severely.

Could it be that by accident someting can press the heatsink sheet metal in direction to the PCB and create some shorts on the board?

I did not get this point will you please elaborate more....

What is the purpose of the two threaded parts blow the the transistors?

One thread region is responsible to hold the PCB by tightening the small screw and other is responsible to screw the base of TEMPERATURE SENSOR (RT4) of DRIVE.

Sorry not to be able to give you a good hint regarding the issues at hand.

Atleast with discussion i am sure i can figure out this problem...

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#22
In reply to #13

Re: Brushless AC-Motor Controller

03/06/2012 1:24 PM

I came back here now that I noticed that I was granted a GA with my earlier answers. I now see the heat sink contact area and the circuit board provides access for the six mounting screws that secure the six power transistors to the heat sink. The lack of smoke marks directly between transistor and heat sink implies that they were in contact with the heat sink but I see something now that really bothers me. Two of your transistors have marks that align with small black circles in your heat sink. It looks like somebody drilled through your heat sink into these two transistors. The holes in the transistors are similar if not identical in size and circular. I would expect an arc through to produce a much more irregular shape. Drilling into a power transistor will destroy many things beyond just the transistor. You have a bigger problem than just this driver.

Good Luck

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#15

Re: Brushless AC-Motor Controller

03/01/2012 11:56 AM

Suggest you analyze system controls for:

1. IGBT gate control PLL timing errors. If the IGBT gates are triggered at the wrong point in time the result is a "phase-to-phase" short through the associated IGBT units and the result will be as ilustrated in your pictures. If unstable check for induced voltage spikes, noise, etc from other components/equipment.

2. If the PLL signal and control is stable and of correct timing; Check your filter network as any filter component failure can allow regeneration voltage spikes to occur that far exceed the rating of the circuit board components/devices. (open or shorted capacitor(s), diode(s), resistor(s).

3. Check for atmospheric contaminents that are causing short-circuit faults. (moisture, chemicals, lint, etc.)

4. Install a voltage recorder on the primary power supply side and monitor for high transient voltage spikes then identify the source of any issues found.

5. Verify the IGBT's are original equipment design compliant as the gate transition timing, reverse voltage impedance , and all other design factors are critical in facilitating proper/correct firing sequence timing events. (OEM specification sheets)

6. Look for abnormal operating events such as multiple pieces of equipment being shutdown/stopped or started at the same time causing supply voltage disturbance.

7. Check your primary power for induced harmonics 5th, 7th, 11th, 13th that can be (are) extremely destructful. The filter usually will have default/standard correction for this however in some cases, rogue harmonics can be present. A high quality oscilliscope can reveal a lot of information in a very short time if used properly.

Good luck, Jim

Register to Reply Score 1 for Good Answer
Associate

Join Date: Apr 2007
Posts: 50
#19
In reply to #15

Re: Brushless AC-Motor Controller

03/02/2012 1:18 AM

Dear Sir,

Your feedback is very much effective please let me know few things ...

1. How i analyse PLL timing Errors...

2. In my DRIVE there is a section of internal power supply which consist of FLYBACK transformer, LM2575 ADJ,VIPER 50SP and Banks of Capacitor SMD type and Inductors... but mostly with these sort of cases transistors BSR14 and BSR16 are also damage which leads towards explosion.. also let me know what is the best way to test the SMD mounted Capacitor(s) open or shorted ???

3. Temperature environment is hotter mostly in my production unit and yes fluffy environment is also there but there, but there are other machines lines (Like Line A and Line B which i describe in my first post) which also covered in these condition but on these lines this sort of incidents are almost tends to zero..

4. Please suggest any best Voltage Recorder for my case...

5. OEM specification sheet of GATE DRIVER CIRCUIT already displayed you can also take a review of it...

Waiting for your favorable reply

Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#20
In reply to #19

Re: Brushless AC-Motor Controller

03/02/2012 4:57 PM

Not to insult your capability or intelligence but I have no way of knowing your level of knowledge of troubleshooting experience/expertise.

Therefore in the interest of safety I must caution you that the risk and exposure you or whomever will be operating the test equipment and performing the analysis is very significant especially when testing on an operating and/or energized control circuit of this type.

Please use utmost care and if you are not absolutely sure of what you are doing, you must not perform any procedure or measurement on an energized system.

This conversation and the procedures are way too complex and lengthy to post in this forum.

CR4 Admin - email address removed

From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers and email addresses posted in threads or comments. You can share this information via the CR4 internal messaging system.

If this is not acceptable, my suggestion is to contact the OEM and have their service department go to you location for support and repair.

Jim

Register to Reply
Associate

Join Date: Feb 2012
Posts: 25
#21

Re: Brushless AC-Motor Controller

03/05/2012 4:51 PM

Hi,

I guess this controller is old.

Are you able to comment on the following:

How old is the installtion and the controller.

Do you have a similar controller running a similar part . If yes then : compare readings for Dc bus voltage , switching sequence and current.

If the motor is the same I would suggest you swap the controllers or the motors .

By using the process of elininaton you can rule out if the cause is from the load or the controller or the motor.

One important question: has this fault been occuring since the begining of the installtion or it just started to happen. If failure has started to happen recently then you need to follow steps up to rule out the cause. If you have a braking resistor then you may need to check it as well. I would also suggest you check regeneration limit and see if the Dc bus gose high, this may be due to a defect in braking circuit .

hope this will help.

cheers

Register to Reply Off Topic (Score 5)
Register to Reply 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bill H. (1); Horrible Old Bat (1); redfred (3); rodeh (1); SHOCKISCAN (2); SimpleMind (2); Tornado (2); uli_newBuilder (2); zohaibmoazzam (8)