Reactive Power

03/04/2012 5:00 AM

1. When does a generator connected to an infinite bus bar imports reactive power?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Reactive Power

03/04/2012 7:17 AM

During loss of excitation

Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Reactive Power

03/04/2012 10:12 AM

Any time the excitation is set so that the generator is operating below unity power factor; i.e., in the lagging power factor area of its capability curve. Loss of excitation is the extreme condition and quickly leads to instability and loss of synchronization with the grid.