Delta Transformer

03/04/2012 3:25 PM

Greetings, If I have 3 167kva transformers connnected in delta and one transformer breaks down, what power can be taken from the remaining system?

Register to Reply
Pathfinder Tags: transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Delta transformer

03/04/2012 3:53 PM

The figure given for this calculation is 58%. This percentage assumes a closed delta bank containing 3 transformers. If three 167 kVA transformers were connected to form a closed delta connection, the total output would be (3 x 167 = 500 kVA). If one of these transformers were removed and the transformer bank operated as an open delta connection, the output power would be reduced to 58% of its original capacity of 500 kVA. The output capacity of the open delta bank is (500 kVA x .58% = 290 kVA). Another figure you will see is 87%. This is 87% of the capacity of the two remaining transformers or 167 x 2 x .87 or 290 kva.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Mar 2012
Posts: 3
#2
In reply to #1

Re: Delta transformer

03/04/2012 4:36 PM

thanks for your prompt response Wareagle. I am an insurance adjuster taking a course to learn more about transformers and AC motors etc but all of this math hurts my head and does not interest me at all as I will never be required to use it. I'm wondering if you could help me out with one more question: A single phase 1 hp motor consumes 9A at supply voltage of 123V at 60Hz at a power factor of 78% while driving a fan. What is the power taken by the motor?

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Delta Transformer

03/04/2012 6:40 PM

quote " A single phase 1 hp motor consumes 9A at supply voltage of 123V at 60Hz at a power factor of 78% while driving a fan. What is the power taken by the motor?"

1 Hp is = 746 watts for the perfect motor. So far we can not build one yet.

So 123 volts x 9 amps x 0.78 pf = 863 watts. This will include the inefficiency of the motor.

what are you planning to do with this type of information?

Register to Reply
Participant

Join Date: Mar 2012
Posts: 3
#5
In reply to #3

Re: Delta Transformer

03/04/2012 6:53 PM

thanks again. I'm just trying to complete a class assignment so all of this info is hypathetical. That is actually the answer I calculated as well so at least it appears I am doing something right!!

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Delta Transformer

03/04/2012 6:42 PM

deleted comment

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Delta Transformer

03/04/2012 7:44 PM

The idea of a class assignment is you do it yourself. That way you learn.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

hillerm0 (2); TonyS (1); wareagle (3)

Previous in Forum: Reactive Power   Next in Forum: Dewatering Pump Motor Starter Panel Drawing

Advertisement