Industrial Refrigeration---Forced Air Cooling Units

03/06/2012 11:10 PM

In an ammonia run refrigerating plant for subzero Fahrenheit cold stores what should be the length and diameter of a finned steel tubing required to build a forced air evaporator to comfortably cool down a cold room 50 feet by 50 feet and 15 feet high from 22 deg C to minus 20 C in the shortest possible run-time?? Cooling load for lights and doors may be neglected or added to the 'size' by 25 % and it may be presumed that the evaporator is equipped with proper condensing capacity.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Industrial Refrigeration---Forced Air Cooling Units

03/07/2012 1:40 AM

I'm sorry, but your question is loaded with misconceptions and makes almost no sense at all.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 287
#2
In reply to #1

Re: Industrial Refrigeration---Forced Air Cooling Units

03/07/2012 2:05 AM

sorry for confusion, i simply asked what length of a finned pipe is needed to cool a certain cold room??

For example, suppose 100 ft of running length of plane pipe/tube of 1/2 inch OD is required to cool a certain room or space from 22C to -20C , then how much of it is required to cool down the same if it is finned, say at 1/8inch distance??

Register to Reply
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Aug 2006
Location: Midwestern United States
Posts: 843
Good Answers: 76
#3
In reply to #2

Re: Industrial Refrigeration---Forced Air Cooling Units

03/07/2012 7:38 PM

This looks like a good place to start. Sorry I can't help you more, but out of my area of knowledge.

__________________
Reuters - Investigators found that the recent thread derailment in CR4 was caused by over-weight creatures of lore and request that membership DON'T FEED THE TROLLS.
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 287
#4
In reply to #3

Re: Industrial Refrigeration---Forced Air Cooling Units

03/07/2012 9:40 PM

Thank you... for the useful link.

Perhaps someone here can tell about the co-relation between the heat flux between a bare pipe and and finned pipe of same dimensions, presuming all other conditions are constant. I don't know whether a formula for the comparative ratio between the two exists???

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#5

Re: Industrial Refrigeration---Forced Air Cooling Units

03/08/2012 3:32 AM

Without knowing how well the room is insulated and how long "shortest possible run-time" means, Guvnor, the scheme will not respond to any calculation.

Why not buy a package from a specialist cold room supplier?

__________________
Good moaning!
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 287
#7
In reply to #5

Re: Industrial Refrigeration---Forced Air Cooling Units

03/08/2012 1:33 PM

As I already stated the room was previously in operation and all conditions were set for performing.Insulation was okay too but no way insulation will hamper the air flow or kill what is called the ''thrust'.

Buying a new package could be a solution if science fails to answer my question!! Friend, sometimes you have to work with your ''hands and feet'' in a poor country like mine!!:)

Register to Reply
Power-User

Join Date: Sep 2010
Location: Orinda, CA
Posts: 249
Good Answers: 14
#6

Re: Industrial Refrigeration---Forced Air Cooling Units

03/08/2012 1:05 PM

Thanks for the interesting problem. Maybe the shortest possible run-time could be achieved by exhausting the 22C air from the ceiling as you feed in -20C air through the floor of the room.

The -20C replacement air could be provided by passing night air through a conduit chilled by suitable means. So instead of waiting for the puny heat flux of fins to take the heat out of a hot room, you dump all of that stale hot air and replace it with fresh cold air. Night would be the best time because your feed is pre-chilled. Your heat transfer operation will be in the confined and controlled space in the cold air feed conduit, a little air at a time with a lot of surface area for heat rejection for that little bit. As the cold air flows in, the hot air will be displaced to the exhaust conduit.

__________________
"Education is lighting a fire, not filling a bottle." -- Plutarch
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 287
#8
In reply to #6

Re: Industrial Refrigeration---Forced Air Cooling Units

03/08/2012 2:18 PM

sorry friend, that's beyond the issue. The problem is air gone static when the height of a room was lowered (to reduce cubic space) when before reducing the room height the same room operated perfectly.

Register to Reply
Power-User

Join Date: Sep 2010
Location: Orinda, CA
Posts: 249
Good Answers: 14
#14
In reply to #8

Re: Industrial Refrigeration---Forced Air Cooling Units

03/09/2012 8:37 AM

So the problem is air gone static. You also say that before the ceiling was lowered, there was no problem. If you had posed this problem as one of air flow and said it was a sealed room cooled by a Blast Freezer that used to be OK before the ceiling was lowered, you might have attracted the attention of the experts on air flow here.

The finned tube question was about heat flux in the abstract, but outside the context of the real problem (air flow) it made no sense. You thought you knew the answer and just needed to find out a few details. Maybe the answer is not in adding a finned tube system but simply installing some fans to assist the recirculating air flow back to the Blast Freezer so the room works like it used to before the ceiling was lowered. That would be easy to try, at least.

__________________
"Education is lighting a fire, not filling a bottle." -- Plutarch
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 287
#9
In reply to #6

Re: Industrial Refrigeration---Forced Air Cooling Units

03/08/2012 2:26 PM

If you have a look at a standard Cold Air Blast Freezer you will note that there is no provision for fresh air intake and the whole freezer chamber is totally enclosed.

The air is thrown into a finned evaporator from axial fans attached to it at the back and discharged air comes out from the opposite open side of the evaporator (ie from the front). Product to be blast frozen such as fish is placed right in front of the evaporator grid. The strong air thrust coming through the evaporator hits the fish and freezes it down to about minus 30 degrees in 10 hours or so, depending upon the thickness of the fish , its initial temperature and the way it is stacked. There is only one door located right in front of the evaporator grid which serves both as entrance or exit .

Register to Reply
Power-User

Join Date: Sep 2010
Location: Orinda, CA
Posts: 249
Good Answers: 14
#10
In reply to #9

Re: Industrial Refrigeration---Forced Air Cooling Units

03/08/2012 4:35 PM

OK, so you dial back the Blast Freezer to a powerful room cooler, then diffuse the blast through a network of nozzles so you have like a carpet of cool air seeping in from the floor. A modification of a known device? Instead of a network of finned conduits disposed within the room, a pressure wave to assist exhaust of the hot air. Air flow will require an exhaust fan, too. Thanks for your lucid explanation of the Blast Freezer. As you can tell, I'm new to this.

__________________
"Education is lighting a fire, not filling a bottle." -- Plutarch
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 287
#11
In reply to #10

Re: Industrial Refrigeration---Forced Air Cooling Units

03/08/2012 10:43 PM

No, you haven't got the point.

Here is a diagram you to show you what a 'blast freezer' is.

Mine has just one door for Loading and Unloading, rest is same.

I hope the sketch now makes my question clear.

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 287
#12
In reply to #11

Re: Industrial Refrigeration---Forced Air Cooling Units

03/08/2012 11:30 PM

Hi friends!

Here is another sketch to make the concept clear.

In the present case the freezer room has one door for loading and unloading and fans are installed behind the evaporator to create the air flow from down up (ie anti-clockwise).

Register to Reply
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Aug 2006
Location: Midwestern United States
Posts: 843
Good Answers: 76
#13
In reply to #12

Re: Industrial Refrigeration---Forced Air Cooling Units

03/09/2012 8:16 AM

Thanks for the additional information. My original presumption was a standard walk in freezer that is more designed to 'maintain.'

Even though I do not know enough about this topic to contribute, I am enjoying learning about 'blast' freezers and the physics of how to rapidly transition non-frozen to frozen.

This thread is becoming educational for me, I hope you eventually find the information you are looking for.

__________________
Reuters - Investigators found that the recent thread derailment in CR4 was caused by over-weight creatures of lore and request that membership DON'T FEED THE TROLLS.
Register to Reply