soft starter

03/08/2012 2:42 PM

Dear Engineers

Kindly explain what meaning an use of Soft starter . what is the deference form the VFD (Variable frequency Drive ) ??????

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: soft starter

03/08/2012 2:55 PM

A Soft Starter is a little bit of a "catch all" term, meaning that several devices may be described that way. But in general, a Soft Starter is something that starts a motor at a reduced voltage for a short period of time. Unfortunately, this also means reduced torque which can be a problem.

A variable frequency drive, on the other hand, provides a higher voltage for higher torque but at a lower frequency that ramps up to the desired frequency. It has the advantage of running a motor slower or faster so that it is unnecessary to change gears or belts, etc.

A lot of manufacturing devices use a VFD because it is a popular approach to begin at a lower speed and then take cost out by increasing speed. Not always a good idea because higher speeds always expose any shortcoming in the design of a process.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: soft starter

03/08/2012 4:37 PM

"Soft starter" usually means a Solid State Reduced Voltage Starter. It uses phase-angle firing of thyristors (SCRs) to only allow a portion of each sine wave to reach the motor, effectively reducing the RMS voltage seen by the motor and thuse reducing the torque and reducing the starting current at the expense of acceleration time. So if it is not necessary to accelerate quickly but it is desireable to accelerate with less current and/or less excess torque, then a Soft Starter will do that. But at the end of it's process, the final result is that the motor is Direct One Line and at full speed / full torque. A Reduced Voltage Solid State soft starter would replace a Star-Delta or Autotransformer starter and do it better with no moving parts and no wear and tear. In particular it is better than Star-Delta because there is no transition spike when changing from Star to Delta, and that has been known to destroy motors and other equipment on-line with it.

A VFD changes the voltage and frequency proportionately to provide full torque capability at any speed. It can do everything that a soft starter can do, and do it better, plus it can change the speed of the motor at any point between zero and full speed. It can also increase the speed beyond the design speed of the motor with proper precautions and an understanding of other conmplex issues that go along with that. But a VFD will cost between 5 and 10 times as much as a Soft Starter, so if speed change is not important to your process, a VFD is not the way to go. If you are going to run at any fixed speed, a VFD adds losses to the power equation and will cost more to operate than just running at full speed. So you should ONLY consider a VFD if there is some other advantage to running at variable speeds.

If you get an "A" on this homework assignment, I expect you to send me US$50 for writing it for you.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Participant

Join Date: Mar 2012
Posts: 1
#3

Re: soft starter

03/09/2012 8:05 AM

Most motor starters are of the Direct On Line type (DOL) which is the simplest and most economical starting mode. However, if the load does not allow a large starting torque or the line supplying the power does not withstand a current of up to 10 times the nominal (10xIn) you cannot use a DOL starter. In this case, an alternative would be to use a Star-Delta starter, which reduces by 3 the peak starting current. However, Star-Delta can only be used whenever the starting load is zero or its torque does not exceed 1/3 of In, and the line supplying the power can withstand the peak starting current.

An example: http://www.schneider-electric.ae/sites/uae/en/products-services/automation-control/products-offer/range-presentation.page?c_filepath=/templatedata/Offer_Presentation/3_Range_Datasheet/data/en/local/automation_and_control/tesys_u.xml&p_function_id=9&p_family_id=141&p_range_id=682&f=F13%3AAutomation%20and%20Control~!F23%3AMotor%20%26%20Motion%20Control~!NNM1:Motor+Starters~!NNM2:On-Off+Motor+Starter~!NNM3:TeSys+U

If this is not the case, then the only solution is to use a Soft Starter. The Soft Starter will supply the motor with progressively increasing voltage. Soft Starters are most suitable for "turbine machines" such as centrifugal pumps and fans. An example of use is in water pipes to avoid the hammer effect that can break the elbows in a water canalisation.

An example: http://www.schneider-electric.ae/sites/uae/en/products-services/automation-control/products-offer/range-presentation.page?c_filepath=/templatedata/Offer_Presentation/3_Range_Datasheet/data/en/local/automation_and_control/altistart_48.xml&p_function_id=1&p_family_id=100&p_range_id=689&f=F13%3AAutomation%20and%20Control~!F23%3AMotor%20%26%20Motion%20Control~!NNM1:Motion+%26+Drives~!NNM2:Soft+Starters~!NNM3:Altistart+48

A Variable Speed Drive is able to start a motor the same way as a Soft Starter but it is also able to increase and reduce voltage in order to control the motor speed at will. Using a variable Speed Drive allows, for example, to vary the speed of a pump in order to increase or reduce pumping according to the need.

An example: http://www.schneider-electric.ae/sites/uae/en/products-services/automation-control/products-offer/range-presentation.page?c_filepath=/templatedata/Offer_Presentation/3_Range_Datasheet/data/en/local/automation_and_control/altivar_71.xml&p_function_id=1&p_family_id=223&p_range_id=1155&f=F13%3AAutomation%20and%20Control~!F23%3AMotor%20%26%20Motion%20Control~!NNM1:Motion+%26+Drives~!NNM2:Standard+Drives~!NNM3:Altivar+71

A Variable Speed Drive is usually much more expensive than a Soft Starter.

Register to Reply
Associate

Join Date: Feb 2012
Posts: 25
#4

Re: soft starter

03/11/2012 5:05 PM

Hi,

an induction motor will draw high currents during startup. One easy way to overcome this issue is reduce the voltage at motor terminals during startup. The most tradiotional way is to use a set of resistors with shorting contacts with timer control. A SS will use thyristors to replicate the effect of the series resistors by controlling the current through the switch ie varaible resistor. Why use SS?.

Look at the application: if you require controlled ramp up or ramp down with inrush redction then you can use a SS. Note SSs donot vary the motro speed.

Once you require speed variation then you move to VSD. A VSD uses sets of switches on replicate PWM signal thus craeting a sinewave which varies in amplitude and frequency to meet your requiremenst.

By maintaining the motors flux optimized , you can achieve full torque at zero speed and 220% rated torque for short time. VSDs are taking a big lead over SS as they are becoming smaller and provide smooth control.

You may contact the Schneider Electric office in DUBAI,or contact me to assist sizing the SS or VSD to meet your application.

You may use the following link:

http://www.schneider-electric.com/site/home/index.cfm/ae/

Register to Reply Off Topic (Score 5)