AC Drive

03/09/2012 4:06 AM

can an AC drive provide fixed voltage more than its input rating?

i e i need a AC drive taking input 400V 3ph & 50Hz & converting it to 480V 3ph & 60Hz.

Please comment...

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: AC drive

03/09/2012 5:38 AM

Some of them can, but you need to check the specifics of each.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#2

Re: AC Drive

03/09/2012 11:16 AM

Here's one:

http://www.sabinamotors.com/v/vspfiles/assets/images/acs800.pdf

Found it on Google...not a paid advertisement.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: AC Drive

03/09/2012 12:54 PM

Don't know where you get that from.

Taken from that brochure:

"Output Voltage 0 to U1, 3-phase symmetrical"

"U1 = Nominal input voltage."

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#5
In reply to #3

Re: AC Drive

03/09/2012 1:33 PM

Oops...got all excited when I perused the tables...

3-phase supply voltage 380, 400, 415, 460, 480, 500. The power ratings are valid at nominal voltage 480Vac 60Hz.

My bad...

He/she would need a multilevel inverter drive...I have no catalog cuts for one at present.

Register to Reply
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: AC Drive

03/09/2012 1:25 PM

VFDs convert the line AC voltage to DC, then fire the DC to recreate an AC output. But the DC voltage it creates from the line cannot be any higher than the Peak voltage of the line. Then because of that limit, the AC output voltage can never be higher than what you can create from that Peak DC voltage. So in general, output voltage cannot be higher than input voltage. The way to deal with it is to use a transformer ahead of the VFD to increase the line input. Simple and clean.

But there are minor exceptions. "Line Regenerative" VFDs, those that have a PWM input instead of a diode bridge, can use their line interactive ability to over charge the bus capacitors just a little bit, maybe 5%. But 400V to 480V is 20%, so even that isn't going to work. Besides, a Line Regen version of a VFD that would have this capability is typically 2X the price of a VFD without it, so a transformer on the input side is always cheaper if you don't need the line regen for some other reason.

Another exception is that in very small drives, as in under 3HP, mfrs can install a "Voltage Doubler" which is a system of caps and diodes that can convert and double the DC voltage ahead of the VFD's own rectifier. I have only seen this in the US market where you want to feed a VFD with 120V single phase and run a 230V 3 phase motor. But as HP goes up, the size of the caps to do this gets ridiculous and a transformer becomes a better option. I have also never seen this done for higher voltages, the capacitor voltage would get extreme.

Thirdly, if you are using a low-harmonic drive such as a 12, 18 or 24 pulse version where you have a phase shifting transformer ahead of the drive, you can use that feature to increase the line input to the drive.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Commentator

Join Date: Dec 2011
Posts: 67
#6
In reply to #4

Re: AC Drive

03/10/2012 12:20 AM

thnx for discussion

Register to Reply