Neutral Currents in UPS Output

03/09/2012 7:16 AM

Dear CR4 users,

We are having single phase UPS it is taking equal amps in phase and neutral. May i know why it is taking so.

Thanks in advance

__________________
key questions why, what & how - just think
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: Neutral Currents in UPS Output

03/09/2012 8:06 AM

Is this a serious question? Electricity travels in a loop, from the source through the load and back to the source. Kirchoff's current law is the rule that explains this in the most basic terms possible. The sum of all currents is zero.

If the electricity takes an alternate path you have what is commonly referred to a fault. This fault could be an unintended path, a short circuit, or a ground fault.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply Good Answer (Score 3)
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#2

Re: Neutral Currents in UPS Output

03/09/2012 11:22 AM

Do you have a motor connected to the UPS?

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Neutral Currents in UPS Output

03/09/2012 4:10 PM
Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#4

Re: Neutral Currents in UPS Output

03/09/2012 4:23 PM
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Neutral Currents in UPS Output

05/05/2023 7:16 AM

It is because the circuit is correctly connected.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

cuba_pete (2); NotUrOrdinaryJoe (1); PWSlack (1); wareagle (1)