03/09/2012 7:40 AM

what is the voltage level in ups (l1 to earth, l2 to earth and l1 and l2) during earthed condition, if it is floting neutral what ìs the voltage above said codition.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#1

Re: UPS Neutral Floating Voltage

03/09/2012 11:09 AM

Whatever the difference of potential is.

Why are you floating the neutral in an UPS? Are you really *floating* the neutral? Do you mean that the neutral is not bonded *in* the UPS? It should be bonded at the service. Is the UPS a separately derived service? Can you explain what you mean by floating?

What is the voltage into the UPS i.e., 480/277, 208/120, etc...?

Register to Reply
Active Contributor

Join Date: Sep 2011
Posts: 14
Good Answers: 1
#4
In reply to #1

Re: UPS Neutral Floating Voltage

03/15/2012 5:45 PM

Yes. No neutral. Transformer is 440/110 (Ph-Ph) Volts. The company spec. purposively called such type. I want to know the reason.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: UPS Neutral Floating Voltage

03/09/2012 3:11 PM

Your post has provide exactly zero information with which to answer your questrion.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#3

Re: UPS Neutral Floating Voltage

03/10/2012 4:39 PM

If the neutral isn't bonded to earth at the source, then the voltage to earth could be anything, Guv.