Non magnetic gland plate is used for Single core Cables. But these cables have got SS Glands. Whether the same is ok?
"Learning new things everyday keeps u healthy"
Pathfinder Tags: gland magnetic single core cable
Re: SS Glands for Single core Cables
03/14/2012 5:06 AM
How about plastic ones, then?
Good moaning!
03/14/2012 6:36 AM
is there any relation between magnetism with insulated cable? don't aware of it !!
Cable gland material selection is based on Surroudings & environment such as hostile salt water situation at offshore area, high & low temp. area, corrosive & acid vapourised extremes etc...................
India - Member - New Member
Good Answers: 164
03/14/2012 8:58 AM
A 3-, 3½- or 4-core cable will carry all three phases (and neutral also in the latter two cases). The vectorially summed up magnetic field around such a cable is zero. So, the gland and gland plate can be of any steel, nothing will happen.
Not so for single-core cables, which carry only one phase. The magnetic field around this can heat up normal steel to red heat. So, one needs non-magnetic glands. Smaller cables can manage with brass glands, but larger ones may require the stronger stainless steel glands. Please note, stainless steel is not completely non-magnetic.
Good Answers: 131
Re: SS Glands for Single Core Cables
03/14/2012 7:38 AM
If by SS you mean stainless steel, you have your answer. Stainless steel generally is not magnetic.
Good Answers: 170
03/20/2012 11:28 AM
To avoid circulating currents due to induced emfs due to stray circultaing currents