Aluminum and Copper Bar Attach

03/14/2012 8:29 PM

Dear Engineers / Electrical Gurus: It is permissible to connect 3600 Amps aluminum bars to 5200 Amps Copper Bars in 480 a.c. Volts Switchgear? What technical or special accessories can be used? How to prevent galvanic reaction? Thanks in advance for your answers

__________________
know it's a treasure
Register to Reply
Pathfinder Tags: ELECTRICAL BUSBARS
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Aluminum and Copper Bar Attach

03/14/2012 8:40 PM

I would worry if you wanted the "3600Amps rated aluminum bars" to carry 5200 Amps.

I don't think corrosion would be a problem at that point.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3
In reply to #1

Re: Aluminum and Copper Bar Attach

03/14/2012 9:43 PM

Sometimes it's easy to get carried away with over-specing a system design when planning for the future.

__________________
jack of all trades
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Aluminum and Copper Bar Attach

03/14/2012 9:40 PM

Assuming your current is less than the lowest current rated joint in your system (in this case say the 3600A bus bar) there are a number of options to ensure a good and tight connection between these metals.

A good place to start is a search of CR4 for busbars (or similar) as this question has been answered a few times.

__________________
jack of all trades
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4

Re: Aluminum and Copper Bar Attach

03/14/2012 9:48 PM

There are conditions that one can safely connect 3600A aluminum bus bars to 5200A copper bus bars. There are also conditions that one should never connect these two bus bars together. I do not have the time nor patience to list all of the conditions required to identify if this is safe or dangerous. Consult the electrical standards and documents for your location.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5

Re: Aluminum and Copper Bar Attach

03/14/2012 11:14 PM

Could you make a drawing to show the proposed setup with typical loads...Generally speaking you can connect copper to aluminum with a conductive grease to protect from corrosion...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Associate

Join Date: Jul 2011
Posts: 48
Good Answers: 1
#6

Re: Aluminum and Copper Bar Attach

03/15/2012 3:08 AM

Tin plate the joint area and you will be fine. No need for us to see drawings etc. This is fairly common, especially in transformer connections where the transformer LV windings tend to be aluminium (cast resign type)

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#7
In reply to #6

Re: Aluminum and Copper Bar Attach

03/15/2012 9:12 AM

I'm still amazed that a group of people that consider themselves Engineers still fall for and promote anecdotal fallacies. Just because you have safely connected these two bus bars together without a problem, does not mean that every joint of these two bus bars is correct.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#8

Re: Aluminum and Copper Bar Attach

03/15/2012 11:48 AM

Use a bimetallic connector,if approved.

__________________
pnaban
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#9

Re: Aluminum and Copper Bar Attach

03/15/2012 3:30 PM

This may add to the confusion http://cr4.globalspec.com/thread/70944

Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#10

Re: Aluminum and Copper Bar Attach

03/15/2012 10:38 PM

Use an approved conductive grease between the two contact surfaces after these surfaces have been sanded with 400 grit silicon carbide paper or cleaned with an abrasive pad and solvent wiped. Bolt the bus bars together and check the bolt tightness periodically. Corrosion won't be a problem if the connection remains dry.

Register to Reply
Register to Reply 10 comments