LV Motor Megger Test

03/14/2012 2:36 PM

dear all would you please let me know about following problem. what would be happen if the LV motor megger test will have done when 2500v @60sec apply between the phase and earth of 400v motor.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: LV motor megger test

03/14/2012 2:43 PM

A good chance of damaging the motor. Normal test voltage is X2 the rated voltage.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#2

Re: LV Motor Megger Test

03/14/2012 4:48 PM

If you were using a Hi-Pot instead of a megger, then you probably damaged the winding insulation; a Hi-Pot is a destructive test (and more if AC is applied).

A megger test won't damage the insualtions since it has very little current capacity and it applies a DC voltage.

As per the specifications of a Hi-Pot test I've read in some manuals from Quadtech that one comon practice is to apply twice the rated voltage of the device under test, plus 1KV, doesn't refer to any standard or norm, it is just something widely accepted.

Regards

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#3

Re: LV Motor Megger Test

03/14/2012 5:27 PM

Handy sheet, thanks.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Associate

Join Date: Feb 2009
Posts: 34
Good Answers: 4
#4

Re: LV Motor Megger Test

03/14/2012 10:51 PM

What would happen - Bang

Go & get a 500V Megger & use that. You do not have to test it for 60sec.

I found the readings on small motors rarely changes after about 15 secs. Usually you will find any problem before that. If it is still moving (generally downward) then the motor is wet - so dry it out.

__________________
Murphy was an optimist....
Register to Reply
Active Contributor

Join Date: Nov 2011
Posts: 19
#5

Re: LV Motor Megger Test

03/15/2012 12:35 AM

Dear Alirahnama,

first of all why you want to take such test, any specific reason?

All the fellow members has responded to your question and You must be satisfied with the answer, but please give your feedback on this!!!

Subhash

Register to Reply
Active Contributor

Join Date: Jan 2010
Posts: 10
#6
In reply to #5

Re: LV Motor Megger Test

03/15/2012 1:02 AM

Dear Subhash,

i have read somewhere on megger tester manual that in DC insulation test there is just some mili amps current beside the stable voltage without any spike so in my point of view this situation could not creating harmful condition or damage the winding insulation.

i think there is difference issues among hi pot test by high voltage Ac current and megger test which is used as diagnostic and is intended to be nondestructive test which could be repeated on the same device.

so i keen on it by use higher voltage ( than regular 500VDC) and time due to getting assure on healthy insulation of winding in absence of some other test.

Register to Reply
Active Contributor

Join Date: Jan 2010
Posts: 10
#7

Re: LV Motor Megger Test

03/15/2012 1:19 AM

thank you so much but i'm not for you.

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#8

Re: LV Motor Megger Test

03/15/2012 2:30 AM

Motor insulation may get damaged if you use 2500 V megger. For a 400V motor 500V megger is recommended. However you can go maximum upto 1000V megger.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Feb 2011
Location: Bristol, UK
Posts: 15
Good Answers: 1
#9

Re: LV Motor Megger Test

03/15/2012 7:38 AM

Interesting. US Gov has a different idea, this is for a post repair test:

"For rewound motors, a DC high potential test shall be conducted at 1700 VDC for motors to be powered by less than 250VAC service voltage. Motors to be powered between 250VAC and 600VAC service voltage shall be tested at 1700VDC plus 3.4 times the machine's voltage rating, e.g. 3264VDC for a 460VAC machine. Readings corrected to 40°C, which are less than 20 megohms, shall be discussed with purchaser."

From http://www1.eere.energy.gov/manufacturing/tech_deployment/pdfs/repair_specs_motors.pdf

So the test should be performed at 3060VDC.

__________________
D.G.
Register to Reply
Power-User

Join Date: Sep 2011
Location: Near the New Madrid Fault. USA
Posts: 269
Good Answers: 1
#10
In reply to #9

Re: LV Motor Megger Test

03/15/2012 8:43 AM

We never "Hi-Pot, PI, DI, or Surge" test with our Baker or Megger over 2000 Volts.

It will show up a "turn to turn, Phase to phase or Phase to ground" fault at that voltage, any higher may damage a motor that has been in service. What you are saying is correct for a Motor Mfg. or Rewind shop standards, the difference is if they "pop" a winding they eat the motor not us end users...

__________________
It's not Rocket Science
Register to Reply
Power-User
India - Member - Justin Anto Engineering Fields - Electrical Engineering - Marks never made me laugh, but good memories did

Join Date: Sep 2010
Location: Thrissur, Kerala, India
Posts: 177
Good Answers: 3
#11

Re: LV Motor Megger Test

03/18/2012 6:51 AM

500V is enough for you.

Refer IEEE 43-2000 for ratating machines for maintenance prpose and for manufacturers.

__________________
If you can't find a way, make one........
Register to Reply
Commentator

Join Date: May 2010
Location: UK
Posts: 89
Good Answers: 2
#12

Re: LV Motor Megger Test

03/27/2012 9:04 AM

If you keep it simple then you'll not go wrong.

try 1000v for 3 mins.

I use it all the time on motors rated at 2000v plus, and that includes the 2000M of cable attached to the motor.

Register to Reply
Associate

Join Date: May 2012
Posts: 52
#13

Re: LV Motor Megger Test

05/15/2012 6:44 AM

oh my !!!! you will destrowing the motor waaaaaahhhhhhhhh 2x the motro voltage only is good <

__________________
i want ot helf piple need assistance and to share my knowleged in technical
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: