Previous in Forum: Electrical Protection   Next in Forum: Use of 5P10 Class CT Instead of PS Class CT
Motor staring on DG set
03/15/2012 4:39 AM
What size ( KW rating ) of motor can safely be started with DOL starter on a single 1250 kVA diesel generatin set at 440 volts/50 Hz output
Good Answers: 22
Re: Motor staring on DG set
03/15/2012 5:00 AM
Thumbrule is the motor rating shall not be more than 25% of the DG rating.
Raghunath
03/15/2012 5:10 AM
An approximate method of estimating the capacity of D.G set is to add full load currents of all loads to be run on D.G Set, then applying Diversity factor depending on your industry, process involved or guidelines correct capacity can be obtained .....
in your case you can go reverse .....!!!
India - Member - New Member
03/15/2012 8:17 AM
Down load sizing softwere available on reputed manufacturer web site.
When was last time you did something for first time.
03/19/2012 3:56 AM
Its also important to know what load your motor is starting and not just the size of the motor.
Good Answers: 170
03/20/2012 11:00 AM
There are many papers published on the subject by leading genset manufacturers like CATERPILLAR, CUMMINS, KOHLER, etc. Pl. do a search.
05/05/2023 6:06 AM
A telephone call to the manufacturer of the <...1250 kVA diesel generatin set...> would be the quickest way to solve this one.
abele (1); dbman (1); electricalexpert65 (1); Happy singh (1); PWSlack (1); raghun (1)