Sound Coming from NER/NGR with Minor Current Flow

03/18/2012 11:09 AM

We have a 6.6kV HT Generation system; the generator is rated at 6.6 kV and 350 amp and it has a 10 ohm NER / NGR connected b/w its star point and the ground. A CT (500/1A) is connected in its path to actuate the Standby Earth fault relay in case of fault.

During normal checking i observed a humming sound from the NER. Using a clamp-meter a current of 1-2Amp was found to be flowing thru' it. A/c to my understanding shouldn't current flow thru the NER only in case of ground fault? Here current is continuously flowing thru the NER in normal condition accompanied by light humming sound.

I want to ask is it normal for current to flow (no matter how small) thru NER during normal operating conditions? and is the sound also OK?

Thanx

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Sound coming from NER/NGR with minor current flow

03/18/2012 1:33 PM

What's a NER/NGR? A/c = airconditioner?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2
In reply to #1

Re: Sound coming from NER/NGR with minor current flow

03/18/2012 3:14 PM

Let's see:

NERNamed Entity Recognition
NERNiger

(ISO Country code)

NERNucleotide Excision Repair

(molecular genetics)

NERNortheast Region

(NPS)

NERNorth Eastern Railway

(Railway in NE England 1854-1922)

NERNortheast Region

(Order of the Arrow, Boy Scouts of America)

NERNorth Eastern Region

(India)

NERNeryungri

(Russia)

NERNational Equipment Register
NERNational Electricity Regulator

(South Africa)

NERNet Enrollment Ratio



NGR

National Grid Reference (UK)

****

NGR

National Guard Regulation

****

NGR

National Grape Registry (UC Davis)

***

NGR

Non Grain Raising (wood finish)

***

NGR

National Geochemical Reconnaissance (Program of Canada)

**

a/c

Nightly Garbage Run (Pokémon)




I think you've got the a/c right. a/c's run on electricity so it must be right.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Sound coming from NER/NGR with minor current flow

03/18/2012 4:42 PM

The amount of current flowing in the Neutral Grounding/Earthing Resistor is an indication of the amount of load/current imbalance in the generator. The vector sum of the three phase currents is flowing through the resistor is indicated by your ammeter, under perfectly balanced conditions it would be zero, otherwise current flows, and don't forget that any harmonic currents may also register.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #3

Re: Sound coming from NER/NGR with minor current flow

03/18/2012 5:08 PM

Thanks for adding some sanity.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: Sound Coming from NER/NGR with Minor Current Flow

03/18/2012 8:28 PM

What is the frequency of the hum? 50, or 60 Hz?

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#6

Re: Sound Coming from NER/NGR with Minor Current Flow

03/18/2012 10:49 PM

With generators, there will be third harmonic currents circulating in the system even without any load unbalance or a phase-to-ground fault, i.e. even during normal 'system healthy' conditions. When generators are part of the system and the neutral earthing is designed to allow over 100A current during earth faults, it is advise to ensure that there is only one system earth. That is to say, in case there is another generator or a grid transformer, the subject equipment neutral shall remain disconnected from earth. This is to ensure that there is no closed loop for the third harmonic currents to circulate. You may like to verify.

With regard to the noise, check for any loose connections in the NER. I don't think the noise should be there if the NER is healthy.

Further, the NERs are generally short time rated. They do have a continuous rating but quite a small value. You may like to verify this as well.

It would be good if you could post the feedback.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Associate

Join Date: Feb 2009
Posts: 34
Good Answers: 4
#7
In reply to #6

Re: Sound Coming from NER/NGR with Minor Current Flow

03/19/2012 1:56 AM

I agree with Raghun. Do some additional checking with a tong type ammeter you may have current flowing that is well below the relay setting. This may be acceptable to you but really it should be zero. Make sure your CT & relay are also connected correctly - you would not like to be missing the fault.

The 3rd Harmonics can show as a hum also but if they are high then your main transformer will most likely be running hot - have a look at the operating temperatures as well.

Feedback would be good.

__________________
Murphy was an optimist....
Register to Reply
Commentator
Pakistan - Member - New Member

Join Date: Dec 2007
Location: PAK
Posts: 68
Good Answers: 1
#8
In reply to #6

Re: Sound Coming from NER/NGR with Minor Current Flow

03/21/2012 10:29 AM

Hey thanx :)

We have four (04) generators each of 6.6kV, 50Hz on single bus; three (03) operate at a time. The NER or to clear any confusion the ''Neutral Earth Resistor'' is rated at 10 ohms, 350 Amp for 10 seconds.

Do you mean to say that only one generator's neutral be earthed and the rest be disconnected, just to stop the circulating harmonic current? wouldn't this lead to other adverse affects?

Would def check again for any loose connections and Trafo operating temperatures.

Btw how is the frequency of hum measured? its just sound isn't it?

Thanx again.

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#9
In reply to #8

Re: Sound Coming from NER/NGR with Minor Current Flow

03/22/2012 8:57 PM

rizwan is right, dont disconnect any neutral-earth bonding in the generators. generators typically come with an internal neutral-earth bond that should not be disconnected.

__________________
BSEE but always learning
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#10
In reply to #8

Re: Sound Coming from NER/NGR with Minor Current Flow

03/23/2012 7:45 AM

That's right Rizwan. Here, NER value is such as to allow 350A current during earth faults. When there is an earth fault in generator stator winding we are talking of ~1000A flowing (3-generator contributing 350A each). As I said earlier you need to keep only one earth connection, disconnecting all other earths. You can check with the manufacturer for his recommendation.

Having said that, the caution is not to leave the system unearthed at any given time. This means an alarm in case of trip of the generator that is providing the system earth and operating procedures to select one of the other generators for star point earthing without loss of time.

__________________
Raghunath
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#11
In reply to #10

Re: Sound Coming from NER/NGR with Minor Current Flow

03/23/2012 9:33 AM

imho, it would make more sense to earth the system at the Main distribution board.

or, leave all generators earthed, but connect together all the ground rods into a grid.

__________________
BSEE but always learning
Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

1capybara (2); KRW43 (1); lyn (3); raghun (2); RAMConsult (1); rizwan (1); SolarEagle (1)