Capacity of Transformer

03/19/2012 12:45 PM

Respected sir,

I am planning a sub station.

Present load AVG POWER is 225 kw continuous.

Feature load is 100 kw continuous

I am planning 500 KVA AS SUITABLE CAPACITY

Shall I go to dry type or oil-cooled?

I am thinking of package sub station also.

The installation is INDOOR.

S.S.Magdum

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: Capacity of Transformer

03/20/2012 7:48 AM

Continuous average power is not the number with which you need to work. You need to look at a site drawing, take a survey of what is connected, based on its ratings, add all of that up appropriately and then factor in some margin for future additions.

You can not make valid conclusions from an average because you have no idea what percentage of a full load that average represents. Guess work is only correct 8.2% of the time. Oh, buy the way, I just guessed at that percentage.

What you have to ask yourself is, "Do you feel lucky?"

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Active Contributor

Join Date: Mar 2012
Posts: 15
#3
In reply to #1

Re: Capacity of Transformer

03/21/2012 2:52 AM

Respected sir,

Thank you very much for reply.

load status is as below.

full load cotinious = 225kw

feature full load continious =80kw

r Total= 305kw

p.f.=.8

Total load in kva= 381kva

(if % loadin 70%), capacity of xmer = 381/.7= 544 kva

say 500kva

This is the way i am calculating .

please guide in this regard

s.s. magdum

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#5
In reply to #3

Re: Capacity of Transformer

03/21/2012 12:25 PM

It looks like you have enough design capacity margin. The main difference between air cooled and oil cooled is the physical dimensions and rate of response to thermal loading. By that I mean that oil will conduct heat away much faster than air.

I believe that oil filled transformers will out perform air cooled in terms of life and protection of the windings. Recently, I learned that a common failure in a transformer winding is on the corner of the metal core. Too tight of a radius created a "hot spot" where the insulation would break down. If my information is correct, an oil filled transformer is a better choice for this problem. As for copper loss, it will be nearly the same for both. But how and where that heat is dissipated can be a problem. Either one will crank out some heat so you need to make sure you have enough ventilation.

An oil cooled transformer may have its own radiator for heat exchange. You might even be able to capture some of that heat to water lines that feed water heaters. I think you will have to check local codes for that possibility. Good Luck!

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Capacity of Transformer

03/20/2012 10:20 AM

From your name, I guess you are from India. If so, you MUST go for ONLY a dry-type transformer for indoor installations, vide the Indian Electricity Rules, 1956. [Rule No. 64 (2) (e) (iv)]. A better chioce would be a packaged sub-station.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Mar 2012
Posts: 15
#4
In reply to #2

Re: Capacity of Transformer

03/21/2012 3:04 AM

Thank you very much sir,

This is a in door instalation.

I am planning for pakaged sub station.

I am worried about cu lossess at hot

conditions whether they are more

than oilcooled xmer ?

please guide in this regard

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); magdumshirish (2); NotUrOrdinaryJoe (2)

Previous in Forum: Problem Related to Earth Fault (Micom123)   Next in Forum: Electrical

Advertisement