Problem Related to Earth Fault (Micom123)

03/19/2012 11:07 AM

Hi all

Warm regards for the day

I work in a thermal power plant wherein my job is to maintain a local distribution system.We have a 415 V distribution system in which we have incorporated a 2 incomer 1 bus coupler scheme. Recently we have charged a 415 V board of the same configuration with the bus charged through an incomer and bus coupler. We are facing a problem over here. The CT used in bus coupler is of 2500/1 ratio and we have a micom123 relay for protection purpose. Once the board is loaded, the relay does not display any current through its neutral but on going through the measurements option present in the relay,one option indicates Ie >>>> (x amperes). The value of the current indicated (x) is varying in direct proportion to the load through the bus coupler. Because of this the bus coupler trips as soon as we start a motor or a battery charger as the value of Ie >>>> becomes exceedingly high . I want to know the possible reasons for such a thing to happen. In case of an earth fault, there should be some current flowing through the neutral. But the relay does not display any current through the neutral as mentioned already.

__________________
mscs
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#1

Re: Problem related to Earth Fault (Micom123)

03/19/2012 12:09 PM

This could be due to

  • missing of one of the phases at the relay
  • wiring a phase CT at the residual current signal input to the relay (wrong wiring)
  • Polarity of one of the phase CTs is wrong resulting in high residual current to the relay

Is the primary injection of CTs and polarity check done during commissioning!

Many times, the actual connections in the panel differ from those shown in the panel drawings and it is important to take time and establish correct ratio, polarity and the wiring to the relay.

Since the relay is in buscoupler panel, presume the relay is measuring residual current and there is no neutral CT input coming to the relay (unlike the trafo neutral CT input to the incomer relay).

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#2

Re: Problem Related to Earth Fault (Micom123)

03/19/2012 11:15 PM

As suggested by raghun

Please check CT connections, and polarity.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#3

Re: Problem Related to Earth Fault (Micom123)

03/20/2012 6:13 AM

maybe its a true earth fault, so current is flowing to ground [earth].

__________________
BSEE but always learning
Register to Reply
Associate

Join Date: Feb 2011
Location: Angul, orissa
Posts: 25
Good Answers: 1
#5
In reply to #3

Re: Problem Related to Earth Fault (Micom123)

03/20/2012 12:16 PM

Well Mr.Capy, if its a genuine earth fault, I do not think the fault current increases in direct proportion to the load. There cannot be an earth fault in each and every equipment which is being switched on.

__________________
mscs
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Problem Related to Earth Fault (Micom123)

03/20/2012 10:24 AM

Micom Relays measure Earth Fault Current from the Zero Sequence Component of the phase current inputs. At the time of motor starting or a battery charger energising, there could be large zero sequence components in the input currents, due to the magnetising inrush current of the motor or the input transformer of the battery charger. Try increasing the time delay of the earthfault element.

Register to Reply
Register to Reply 5 comments