Dear All,
I am working with one of the contracting firm
Our Electrical consultant has indicated TPN breakers (4000A, interlocked) for connecting to load. (No isolation of the neutral)
The system has two source of supply.
A. First sources, is from 2 transformers of 1250 KVA,11kv/415V. Both the transformers have Incomer of 2000A connected to a common Bus. This Bus is inturn, connected to Incoming of 4000A TPN ACB.
B. Second source is from the Generators. 3 Generators of 1000KVA (LT) running in parallel & have their own brekaer. These 3 Generators are also connected to another common bus. This common bus is inturn, connected to incoming of 4000A TPN.
In PCC, these two 4000Amp ACB are on either side & at the centre all loads are connected.
Both these TPN 4000Amp ACB are interlocked. only one will "ON" at a time.
Both neutral are connected.
My question is : Is it right thing to use TPN ACB instead of 4 Pole ACB, where we are using two source of supply?
I feel we should go for 4 Pole ACB instead of TPN ACB for safety. But I dont have any evidence to proove it. I request professional advice, is there any guide line or mandatary rule, insisting for 4 pole breaker for neutral isolation in such condition?
Regds.