As i know earthing aim is to reduce the resistance of earth to provide a path for the fault current.this is done by increasing the number of electrodes and several methods.
But i read that we must increase the resistance of earth (example by adding rocks)in order to decrease step and touch potential
can anybody clear this conflict for me ?
Re: Earthing
03/27/2012 4:18 AM
Go with the first sentence.
Re: Earthing
03/27/2012 6:44 AM
first sentence is related to below ground level...
second sentence is related to above ground level...
Now tell me where is the conflict...!!!
"Learning new things everyday keeps u healthy"
Re: Earthing
03/27/2012 8:30 AM
so what ?
both are added to calculate ground resistance
Good Answers: 170
Re: Earthing
03/27/2012 10:20 AM
Well! Let me try to explain further! The resistance of the earth is kept low (a rightly said in a previous answer) below ground so that fault current passes through the natural earth only back to the source and not thro any other path which could harm any human/animals/equipment/installation.
If a living being happens to stand on the natural earth, while fault current flows thro it (the natural earth), current diversion would take place thro the body of the living being and could cause harm (even death) to the living being. To reduce such a possibility, you increase the contact resistance between the feet of the living being and the natural earth on which it stands. One way of doing this is to fill up the natural earth with a high resistance material like crushed rock.
Hope it is clear now.
Reply Good Answer (Score 6)
Re: Earthing
03/28/2012 4:09 PM
Quote "As i know earthing aim is to reduce the resistance of earth to provide a path for the fault current"
Please don't say that.
There is confusion when you use the term earth. Are you referring to earth(dirt) or are your referring the the neutral of the system. An earth(dirt) fault has a high resistance and current flow is a low value. A Phase to neutral(sometimes called ground) fault will have a low impedance and the current flow is a high value. Regarding distance, the fault will flow back to the source. Earth(dirt) is not a "sink hole" and does not absorb the fault current.
Earthing , per the OP seems to mean a connection to mother earth(dirt). Earthing a piece of equipment will not provide safety in the event of a fault. The resistance of the earth is too high to allow enough current flow to trip a breaker. Bonding or grounding the equipment is the method used in the US to cause the breaker to trip. An Equipment Grounding Conductor EGC is installed with the power conductor and connected to the equipment. The EGC is bonded to the metal frame at one end and to the Main Switch and grounding electrode at the other end. This provides a path for the fault current to flow.
Re: Earthing
04/05/2012 11:49 AM
In a substation
earthing pits are made which have an electrode which is buried deep into the ground . there can be many earth pits .
in a 66kv substation where i worked during its construction there were three separate earth pits for Surge arrestors .
and two separate earth pits for earthing the neutral of the secondary side of the delta star step down transformer
also Galvanised Iron strip was layed across the ares of switchyard .this net was connected to some more earth pits . In the end the switchyard was cover with big balck gravel .