Transformer & Generator selection for motor loads

05/07/2007 10:47 PM

Dear Sir,

What is the standard practice to select Transformer and Generator capacities for large motor loads with soft starters? What could be the additional % capacity has to be allowed for motor loads due to their start up currents?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Transformer & Generator selection for motor loads

05/09/2007 12:53 AM

The sizing depends on the inertia to be accelerated by the motor. If it is a pump or fan then 133 to 150% KVA compared to KW is OK. For crushers and conveyors 200% is suggested. This assumes that the voltage regulation on the HV side of the transformer is not excessive on start. Remember a soft starter is a soft mechanical start but still draws a lot of KVA as the squirrel cage induction motor has a power factor of only 0.3 on start up so it takes a lot of KVA at 0.3 to produce the KW required to accelerate the load.

Register to Reply
Guru

Join Date: Jan 2007
Location: Sitting directly behind my keyboard in Albuquerque - USA
Posts: 592
Good Answers: 19
#2

Re: Transformer & Generator selection for motor loads

05/09/2007 7:09 AM

Any large supplier such as Cat, Cummins, etc., has free software available to size generator sets The software depicts the voltage dip, engine power (speed droop) based on inputs of motor code, soft start, altitude, ambient, humidity, etc. If this is a large machine, such as 2-3 MW, then you need to get scientific with this and get into the reactance available of the generator. Remember that active power (watts) affects engine power availability and recovery ability (the governor, speed, fuel type, turbocharger curves, etc) and reactive power (VARs) affects the load of the generator [alternator] (heat via magnetism). The engine doesn't 'feel' heavy VAR loads, but the generator does. Heavy VAR loads will cause large voltage dips and overcurrent. Heavy watt loads will cause engine speed drop, overload, exhaust temperature rise and it simply may not recover and melt pistons in 2 minutes time.