Restricted Earth Fault & Standby Earth Fault Relay

04/03/2012 6:20 AM

My 3MVA transformer is sensing out side of zone fault but REF relay tripping others not.

Kindly suggest me why this is happening?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Restricted Earth Fault & Standby earth fault relay

04/03/2012 6:30 AM

One explanation is that there is an earth fault greater than the trip setting of the restricted earth fault relay. Nothing else can be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Restricted Earth Fault & Standby Earth Fault Relay

04/03/2012 11:17 AM

Are CTs matched perfectly? Is there a stabilising resistor? Has it been properly set?

Register to Reply
Participant

Join Date: Apr 2012
Posts: 2
#3
In reply to #2

Re: Restricted Earth Fault & Standby Earth Fault Relay

04/03/2012 11:44 PM

All CTs are matched.

Stabilising resistor is set as per recommended setting.

Register to Reply