Water Levels In Batteries

04/03/2012 11:13 AM

We just replaced the batteries in out hand trucks and we find that the batteries need to be refilled on a daily basis.

We do charge the batteries every night and the machine do get a lot of use.

These are 6 Volt commercial 3 Cell lift truck batteries there are 4 of them in each power hand truck.

Do you think that the batteries using this much water, 400 to 600 ML per cell per day is normal ?

Thanking you in advance for your answers...

Ross

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Water Levels in Batteries

04/03/2012 11:27 AM

At first blush, it sounds like the batteries are being overcharged and evaporating/boiling the water.

Check that the charging system is working properly.

Register to Reply Good Answer (Score 2)
3
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Water Levels in Batteries

04/03/2012 11:31 AM

You may be losing water during charging process...ie:overcharging..or the batteries may be getting old, or other reasons...you might want to try 'battery equalizer'....or 'battery chem'...or thermoil..

"Battery Equaliser the Solution for Internal Resistance & Sulfation:

Lead acid batteries have changed very little in 70 years. From the initial application of the electrolyte, sulfation begins coating the lead plates causing internal resistance. Aging batteries lose overall performance and require increased maintenance (more water) and charging time. Sulfation will eventually choke out any electrical activity. Stored and inactive batteries accelerate the problem of sulfation, leading to REDUCED BATTERY LIFE.

A small amount of Battery Equaliser reduces resistance and sulfation. Add Battery Equaliser to each cell will mix with the existing electrolyte solution. The improved battery chemistry will dissolve existing sulfation and prevent new deposits from forming for years to come. Batteries will charge faster, hold a charge longer, reduce terminal corrosion and reduce gassing (water consumption). Follow normal battery maintenance and DOUBLE BATTERY LIFE WITH ONLY ONE TREATMENT."

http://www.ehow.com/how_8116374_instructions-battery-charging-forklifts.html

http://www.batterychem.biz/

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 3)
Guru

Join Date: Jan 2011
Posts: 668
Good Answers: 3
#3

Re: Water Levels in Batteries

04/03/2012 12:10 PM

the batteries are being over charged. batteries should never need to be re-filled after every charge. i only check mine every few months and never had to add water. boiling battery acid during charging will ruin them in short time.

my best guess would be that the batteries are connected in series [not enough information] resulting in 24v output to drive a 24v motor. check that the battery terminal are connected in series. run "plus to negative" across all eight terminals. i may be wrong. check with the manufacturer reguarding the wiring of the batteries and the correct charger. it will save you alot of money and headaches.

Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#4

Re: Water Levels In Batteries

04/03/2012 1:07 PM

Are ALL batteries that are forced to work in series identical? Do they ALL need about the same water amount or some need less? Was the initial acid filling and preparation done by an expert or did you have to Google? Do you have any data about nominal capacity (Ah), initial charger applied current (when battery is at most discharged state), final voltage (at full charge) and average temperature the battery is working in? Do these data comply with battery manufacturer data that I assume you were provided with, when got the new batteries? Without some real data only astrology could help, but we would still need exact birth (or manufacturing) dates. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Active Contributor

Join Date: Aug 2011
Posts: 15
#5

Re: Water Levels In Batteries

04/03/2012 1:34 PM

Additional INFO

Batteries are deep cycle US2000 XG made by US BATTERY CORP the AH rating on them is 216 AMPS

They were purchased by from a distributor filled and the specific gravity when fully charged is correct

They are wired to 4X the voltage

I has asked the manufacture about the charging rate of the on-board charger that is within the walker. Will advise when they get back to me.

The water level seems to drop consistant among the cells

Ross

Register to Reply
Power-User

Join Date: Mar 2012
Location: Hot Humid Houston
Posts: 229
Good Answers: 29
#6
In reply to #5

Re: Water Levels In Batteries

04/03/2012 6:02 PM

Based on this information, it seems you have a charging system problem rather than an a battery problem.

I suspect the battery charger has a failed voltage regulator or cut-off and your batteries are being overcharged, which boils off your water in equal amounts on all batteries.

This is a volt problem, not an amp problem, so you can easily measure while charging.

Get the info from the truck manufacturer and you could have a simple part-exchange fix.

__________________
txmedic3338
Register to Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#8
In reply to #5

Re: Water Levels In Batteries

04/04/2012 11:22 AM

Most material handling equipment the chargers are spec for 6 hr charge rate. As the others have said sounds like they are being over charged. What you describe sounds like a pallet truck that has four GC4 or GC3 batteries. What they use in golf carts. So a 24 dc system. Finish dc voltage should be around 29 vdc. You should also take voltage reading across each battery to see if the have the same voltage drop. You might want to check to see if the charger has an equalizer setting and it's not used every charge. Or that the switch that turns it on and off is functioning. Also when checking the finished rate dc voltage switch the meter to ac. Ac current should be in millivolts. Some times the rectifiers can break down the ac current will over heat the batteries causing fluid lost.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Power-User

Join Date: Jan 2010
Location: Atchison Village
Posts: 383
Good Answers: 39
#7

Re: Water Levels In Batteries

04/04/2012 3:21 AM

Minimum time from full discharge to full charge for lead acid is ten hours. Make sure your workers put them on charge ASAP. You're gonna get maybe a year of life out of a set with full cycles like that. 300 full cycles is pretty much standard. Of course, check the voltage and current. The good chargers are three step or more. If you're running two shifts, the batteries are doomed. Eight hour charging will damage the plates and boil off the water (and probably coat everything in the area with sulfuric acid powder, for example control electronics, cables, connectors etc.

__________________
Align culture with nature...
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2010
Location: India
Posts: 166
Good Answers: 1
#9
In reply to #7

Re: Water Levels In Batteries

04/05/2012 8:49 AM

While,it is evident that you are overcharging batteries leading to electrolysis of water, with hydrogen and oxygen escaping to atmosphere. You can measure the gravity of electrolyte by a hydrometer,every hour to see when consecutive gravity readings are same.That should be end of charging. Also look at charging voltage9( should be close to 2.4Volt per cell.Check if the charger is constant current type initially and then change to constant voltage after a set time. It could be that the constant current charger is continuing charging leading to over charge. The equalizing charge is a low Ampere charge at a little higher voltage to take care of sulfates on plates. There are other inputs on it above.

The biggest danger you have is very low life of batteries due to active material in positive plates getting disengaged from the grid. due to over charging. That will be expensive and you will have to replace batteries. So move fast.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Apr 2012
Posts: 75
Good Answers: 6
#10

Re: Water Levels In Batteries

04/07/2012 11:48 PM

That is GROSS overcharging. 16 volts or more. SLA battery electrolyte loss starts to become noticeable at 15.2V by my tests in motor cycles.

That fast a loss, id expect 16.5 -17V.

And torched batteries.

Get a profiling charger as Schumacher sells. Batteries are too expensive to burn down like that with a cheap charger. They have a charger thats ideal for the Exide GC series, I designed a custom system for one application using their dual marine charger.

for a commercial application, get profile data from the battery mfgr and find the CORRECT charger (with charge profile that matches the battery).

AND- monitor battery TEMPERATURE WHILE IN USE.. just in case. It would be bad news to have a high drain in use and have a battery explode.

Register to Reply
Associate

Join Date: Mar 2012
Posts: 31
Good Answers: 1
#11

Re: Water Levels In Batteries

05/09/2012 10:23 AM

Water loss is one indication of over charging, discoloration of electrolyte (should be crystal clear), and temperature rise are other symptoms. If you enter the space where the charging is taking place, and are overwhelmed with the smell of sulfur; your batteries are cooked (toast), and may require replacement. One of the best ways to prevent over charging (until you can acquire a charger with the correct algorithm to match your batteries) is to utilize a timer to stop your charger. This will require some knowledge as to the end voltage for charging, and the depth of discharge after each usage to determine (estimate and set) your charging time.

Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

daveca (1); durtieduck (1); Guest1947 (1); lyn (1); ormondotvos (1); ozzb (1); Rossm (1); SimpleMind (1); SolarEagle (1); Thomas J. Becker (1); txmedic3338 (1)

Previous in Forum: Solid Smoke With Helium?   Next in Forum: Letter Of Credit

Advertisement