Commentator

Join Date: Nov 2009
Posts: 89

Surge Protection

04/13/2012 9:40 AM

I want to install a surge arrester in the input power to a lighting panel; but according to the mark-up given; a 16amps breaker was used upstream the surge arrester after looking at the manufacturers specification, i realized a backup fuse was recommended upstream instead. Please is it possible to replace the fuse with a breaker as this is what the client wants.

Surge Protection Specs: VAL-MS BE Order No.: 2817741

Nominal Voltage: 230V AC

Arrester rated voltage: 275V Ac

Frequency: 50Hz

Breaker to be included: 16amps C-curve

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: Surge Protection

04/13/2012 10:36 AM

As you probably realize, what the client wants is not necessarily what he needs. If you give him what he wants, he will hold you responsible for the failure. I personally really dislike being in that position.

When it comes to surge protection, you need to qualify what kind of surge it is that the customer is concerned about. There are different solutions for the different types of surges.

Short duration spikes can be addressed by a number of surge arrestors designed to short out the overvoltage for the duration. Usually for those, the higher the current rating, the better. It is not uncommon to find such devices rated for 20,000 Amps.

Realistically, that level of current will vaporize most conductors if it persists for long. Other types of spikes that last longer might be more favorably addressed with a power line filter if you don't have to worry about harmonic distortion. Perhaps just a line reactor will serve the required purpose. They are cheap and don't need fuses or circuit breakers.

I think if you do some research you find that most circuit breakers are slower than fuses because mechanical motion makes it so. Perhaps a better choice is something that uses a gas discharge tube or even a resettable fuse as necessary. All of these devices represent certain choices.

While I didn't stumble upon Order No. 2817741 I did see some earlier versions that imply what is being thrown around. I suppose each order is designed to work within its own frame of tolerance. And, while that may work for a given type of surge, does it really describe the exact problem about which the concern has been expressed?

I encourage you to first understand the problem and then talk to your customer.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Nov 2009
Posts: 89
#2
In reply to #1

Re: Surge Protection

04/13/2012 12:02 PM

So sorry, the ful specification is

Surge Protection Specs: PHoenix Contact (VAL-MS BE Order No.: 2817741)

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#3
In reply to #2

Re: Surge Protection

04/13/2012 2:12 PM

OK, now the full spec. search worked. Looks like you need to call the mfg. applications engineers. I must say, I can't understand the purpose of the fuse...

Most surge protectors just turn black when the"ve had enough.

NYOJ

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#4

Re: Surge Protection

04/13/2012 4:42 PM

The fuse or circuit breaker are for protection from one of the common failure modes of MOV-based surge arrestors : once the cop a decent surge they can fail short-circuit.

It shouldn't make much diffierence if the protection is a fuse or a CB, but the manufacturer's recommendation is the trump here.

Some brands of surge arrestor have an internal fuse which mostly eliminates this issue.

__________________
paulusgnome
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#5

Re: Surge Protection

04/13/2012 11:11 PM

The essential answer: what the customer wants, is not necessarily what the customer needs.

Register to Reply
Associate

Join Date: Oct 2011
Posts: 29
Good Answers: 2
#6

Re: Surge Protection

04/14/2012 4:54 AM

VAL MS has an internal feature of THERMAL DISCONNECT, which electrically isolates the plug after its service life, and ensures NO SHORT CIRCUIT during failure, atleast I am yet to come across one.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Apr 2012
Posts: 75
Good Answers: 6
#7

Re: Surge Protection

04/14/2012 4:56 PM

Having done that kind of engineering:

1.) fuses and CBs ARE NOT SURGE ARRESTORS.

2.) fuses and CBs are NOT the same thing and are NOT interchangeable. They do different things. A 100 amp breaker will pass MUCH more current than a 100 amp fuse. I once tested a 30 A automotive breaker, it tripped at 100A in about 3 seconds.

3.) Client has what reason for "wanting that?" CLient will get really tired of replacing fuses that blow when there is no fault.

Fuses and CBs limit LOAD CURRENT. They are in SERIES.

Suppressors limit TRANSIENT VOLTAGE and are in PARALLEL to ground.

Lacking even this basic knowledge, you should not be working on this system.

Register to Reply Score 1 for Off Topic
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#8

Re: Surge Protection

04/16/2012 3:22 AM

@Benotype, For sure, it is possible to replace fuse by circuit breaker to protect a Surge Protection Device (SPD). Those short circuit protective devices(SCPD) must be coordinated with the SPD upstream. To know which exact type of circuit breaker do you need, it is necessary to know the characterist of VAL-MS cartridge (because your reference is the base element alone)If the SPD cartridge is Imax=40kA(8/20) MCB type could be C curve 16A but this information has to be confirmed by the manufacturer
For more information, I let you read the "Wiki EIG" chapter "Protection against voltage surge in Low Voltage" with the link below:
http://www.electrical-installation.org/enwiki/Detailed_characteristics_of_the_external_SCPD

Register to Reply
Commentator

Join Date: Nov 2009
Posts: 89
#10
In reply to #8

Re: Surge Protection

04/16/2012 5:03 AM

Thank you all for your immense contribution. Thank you obouill for the link you added to your thread. it was very,very,very rich. Thanks

Register to Reply
Commentator

Join Date: Nov 2009
Posts: 89
#11
In reply to #8

Re: Surge Protection

04/23/2012 8:53 AM

Thank you very much for your contribution. I'm almost done with the job but have a littlle question to ask you. In a three phase and nuetral connection, will it be possible to use varistors and gas discharge tubes surge protection device rated at nominal 230V and arrested rated volatge of 275V? Or probably a rated nominal voltage of 400V and arrested volatge 0f 440V.

From my research i have only seen nominal voltage 400V MOV used in three phase supply without nuetral. I just want to be sure.Thank youvery much

http://www.electrical-installation.org/enwiki/The_components_of_a_SPD

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#12
In reply to #11

Re: Surge Protection

04/23/2012 12:22 PM

The link you included in this reply shows three voltage limiting varistors in line with each of three phases, tied together on one line and then in series with the gas discharge tube. It would need to be close to your point of connection (power hookup) to be effective. Every 12 inches of leadwire between the devices and the power connection de-rates the overvoltage protection by about 500 volts peak.

Perhaps what you were looking to understand is that the gas discharge tube becomes conductive at some given voltage and acts very much like a switch. That also means that its impedance changes from very high to very low in a matter of microseconds. The Varistors (voltage limiting devices) retain a substantial amount of resistance but it decreases rapidly beyond a certain threshold. That absorbs some of the energy in the surge but it can only handle some percentage of the surge. The more (in parallel) the better.

You also need to remember that in any AC power system, your stated voltage is the RMS value. For a single phase peak voltage, you must multiply the RMS value by the square root of two or 1.414. In a three phase system, you can treat the phase to neutral loads as single phase but for a phase to phase connection (or device) it requires an RMS multiplier of the square root of 3 or 1.732 for the normal peak voltage. Consequently, as shown in the example in your link, the varistors for your 230 Vrms system would be rated at 400 volts and the gas discharge tube would be rated at a fairly low (limit above normal) voltage (say 40V?).

Lastly, you need to remember that these components don't last forever, especially if they have to work very hard. You can put several varistors in parallel in order to survive longer. When they quit working, they usually fail in a high resistance (nearly or actually open circuit) mode. If you find the right kind, they will change color when they reach end of life.

You may expecting to build a surge supressor at some savings to yourself. This will not be the case unless you buy in quantities of several thousand components at a time. If this is a one time effort, you will spend less by just buying a standard surge supressor from some manufacturer that purchases his components that way. And he will know how to put them together to really get the benefits.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Surge Protection

04/16/2012 3:25 AM

Engineering isn't about giving Clients what they want. It's about giving them what they can have.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

benotype (3); daveca (1); leveles (1); madhavdivya (1); NotUrOrdinaryJoe (3); obouill (1); Paulusgnome (1); PWSlack (1)

Previous in Forum: Mems Gyro Mass Unbalance   Next in Forum: Switch Mode or Transformer Type UPS?

Advertisement