How to Change Generator Reactance Value to %

04/15/2012 9:58 PM

Hi Guys,

I have currently a generator with me with the reactance in per unit value.

Take for instance, the if Direct axis synchonous reactance is 1.9226 per unit.

Does this means that it is 192.26%?

Please Help !

Thanks !

__________________
There is no limit towards how much one can learn.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: How to Change Generator Reactance Value to %

04/15/2012 10:50 PM
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: How to Change Generator Reactance Value to %

04/16/2012 9:09 AM

Yes! It does mean that the Direct Axis Synchronous Reactance is 192.26%, which means that the intenal voltage drop within the generator windings with rated load at rated power factor, will be 192.26% of the rated terminal voltage, which also means that the EMF generated by the generator will be 292.26% of the rated termial voltage.

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3

Re: How to Change Generator Reactance Value to %

04/17/2012 10:20 PM

The generator reactance is 1.9226 per unit means the calculated per unit value of the generator is 1.9226 with the base value of the generator's rated KVA and rated voltage.

For example, the generator is assumed 5 MVA, 11KV, 3 phase. For this case, the base KVA is 5000 and base KV is 11 (L-L).

For this system,

The base impedance (Zbase) = (Base KV)2 x 1000 / Base KVA

= (11x11x1000) / 5000 = 24.2 ohm

The actual reactance of the generator

= base impedance (Zbase) x per unit value = 24.2 x 1.9226 = 46.53 ohm

Hope it helps.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)