Analog Output Point in Honeywell DCS

04/17/2012 12:42 PM

I would like to know why it is required to inactivate the Analog output point in Honeywell TPS/TDC 3000 DCS before disconnecting the cable from the positioner.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Analog output point in Honeywell DCS

04/17/2012 12:48 PM

To avoid damaging the unit....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Active Contributor

Join Date: Aug 2011
Posts: 10
#2
In reply to #1

Re: Analog output point in Honeywell DCS

04/17/2012 12:52 PM

Can you be specific what will happen?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: Analog output point in Honeywell DCS

04/17/2012 1:18 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#4

Re: Analog Output Point in Honeywell DCS

04/17/2012 5:40 PM

Speculation on my part because I don't have access to a Honeywell DCS, but there's clues.
I suspect that an analog output will not sustain any physical damage. DCS hardware is pretty robust and most current AO's can regulate its output across a short circuit and not whimper.
AO's do things like drive valves, VFDs and damper drives and the loss of a valid drive signal should be an alarmable event.
A DCS is very alarm intensive by design. So I suspect that the "disable/inactivate" requirement is probably related to the probability that the DCS will detect an open circuit on the AO when the wires are removed and trigger an alarm.
Along those lines, Honeywell's XYR6000 wireless clearly has links to their DCS, as evidenced by earmarks like the necessity to configure any point into OOS (out of service) mode before making any changes. Iris

Register to Reply
Active Contributor

Join Date: Aug 2011
Posts: 10
#5
In reply to #4

Re: Analog Output Point in Honeywell DCS

04/17/2012 11:01 PM

Thanks for the reply. Your assumption might be correct. when we remove any AO point wires defenitely DCS will create an alarm. My concern is what else will happen other than this alarm. Normal alarm does not make any effect on system. So other than this alarm any severe problem could happen or not?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #5

Re: Analog Output Point in Honeywell DCS

04/18/2012 3:01 AM

What did Honeywell say in response to the telephone call?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Oct 2007
Location: Canning Vale Western Australia.
Posts: 160
Good Answers: 7
#6

Re: Analog Output Point in Honeywell DCS

04/17/2012 11:51 PM

Honeywell DCS output cards especially the older ones have a habit of putting out a card failure signal and dropping the other outputs on the card to zero. ie entire card can go belly up even though only one output should show to be faulty.

As you should know this is a bad thing if it is controlling a large process and I know because I have done it, it dropped out a 200t/h steam boiler. All the outputs went to BP(bad point)and I went to the dog house.

__________________
I attend work so my dogs can have the good life.
Register to Reply
Active Contributor

Join Date: Aug 2011
Posts: 10
#10
In reply to #6

Re: Analog Output Point in Honeywell DCS

04/18/2012 12:26 PM

I agreed with you. Once we got the same problem when we removed an analog output with out inactivating the point, all the outputs connected to that particular card has got initialized on its controller. But we could returned back that loop immediately and saved the other controllers. Now i need to know that how the card detects the failure of one output and putting other to a initialized condition?

Register to Reply
Commentator

Join Date: Dec 2007
Location: texas
Posts: 92
Good Answers: 8
#7

Re: Analog Output Point in Honeywell DCS

04/17/2012 11:57 PM

Hi,

inactivating an analog output point is not "required" before disconnecting the wires, but you will get a system status alarm when the wires are disconnected. No damage will occur.

Thanks

__________________
"The older I get -The better I was"
Register to Reply
Commentator

Join Date: May 2011
Posts: 61
Good Answers: 1
#9

Re: Analog Output Point in Honeywell DCS

04/18/2012 6:31 AM

Positioner of any control valve or other controller reports the position of that particular controller. If you open the wire connected to positioner without proper precaution, the controller may get confused about its position and in turn it will malfunction, either fully open or close.

Register to Reply
Associate

Join Date: May 2012
Posts: 26
#11

Re: Analog Output Point in Honeywell DCS

05/18/2012 7:09 AM

Sir

i am working on same honeywell DCs C300 EXperion inactive the AO channel is neccessary to protect the card output signal from grounding ,because when open the wire there aree chance the wire get touch the positinor body & card can damage or fuse blow