Intrinsical Safety Barrier and Isolation Barrier

04/18/2012 7:02 AM

What is difference between intrinsic safety barrier and isolation barrier?WHich can be used for DI,DO,AI,AO?

__________________
Chakradhar.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Intrinsical safety barrier and isolation barrier

04/18/2012 7:25 AM

A1) An isolation barrier maintains galvanic isolation between the hazardous area wiring and the safe area wiring whereas the other type does not, which may be important depending on the type of instrument connected.

A2) Both types can be used, though it depends on what the device is connected to as to the correct type. In each case, follow the instrument manufacturer's instructions to the letter.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#2

Re: Intrinsical Safety Barrier and Isolation Barrier

04/18/2012 10:49 AM

For DI,DO,AI,AO isolation, separate with an isolation barrier.

If you are routing cables in tray, use of an isolation barrier (divider) between your digital/analog I/O will be fine.

If in conduit, separate D/A conduit systems is a must.

If in a panel, individual Panduit channel to separate the looms will suffice.

If you are in a classified area, tray cable sealing glands and/or conduit seal-offs are a must.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Register to Reply 2 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!

Previous in Forum: Level Gauge and Transmitter for Buried Vessels   Next in Forum: Temperature Transmitter-Configuration Setup

Advertisement