Unbalanced Load

05/09/2007 9:32 AM

My question is in regards to an unbalanced load. To my understanding a three-phase balanced system is that the phasor sum of the three line or phase voltages is zero, and the phasor sum of the three line or phase currents is zero. When the three load impedances are not equal to one another, the phasor sums and the neutral current are not zero, and the load is, therefore, unbalanced. The imbalance occurs when an open or short circuit appears at the load.

Can someone give me an example of an unbalanced load from there experience?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: unbalanced load

05/09/2007 9:38 AM

Yes when a local tranformer blew up because of a fault in its windings. Big bang lots of smoke then sirens, more sirens then silence. several thousand went without power for several days.

Register to Reply
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#2

Re: unbalanced load

05/09/2007 10:18 AM

We had a large air 3 phase air conditioning unit lose one phase. The unit ran faster but noisier. Everyone just stood around looking at it. They new something was wrong but did not know what, since to the observer, it was still operating. It even seemed to operate better (faster) than normal.

The extra vibration and heat would have eventually destroyed the unit if we had not shut it down. This is interesting since the protection ccts would not have protected it. The result again would have been a Bang, Smoke, sirens... as guest said in reply 1.

__________________
Perfection is a subjective and abstract concept.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: unbalanced load

05/09/2007 4:06 PM

Generally a three-phase piece of electrical equipment (eg- a 3ph motor) will be designed to balance out the load over the three phases. Problems can occur when you have a system that uses 3ph and neutral, where part of it runs off 3ph (and is balanced) and another part runs of a single phase (using the neutral).

As a better example, consider a large factory powered by its own transformer and using mostly 3ph motors but also lots of large single phase loads connected across only one of the phases (transformer imbalance occurring, but not due to a fault). Generally thou the single phase loads would be spread over the three phases.

Another example of a unbalanced load occurring due to a fault is when a 3ph motor drops a phase. Not nearly as spectacular as a transformer failure due to a winding short thou (but that technically isn't due to imbalance, rather fault current).

__________________
jack of all trades
Register to Reply
Active Contributor

Join Date: May 2007
Location: UMR soon to be MST
Posts: 17
#4

Re: Unbalanced Load

05/10/2007 1:10 AM

it depends on what your loads are...if you have many single phase loads that are not evenly distributed between the 3 phases or if you have highly inductive or capacitive loads all in total your 3 phases will not balance well. what type of loads are you running? what does your power factor look like?

__________________
I know how to google and find things online, thanks; Just answer the questions given.
Register to Reply
Anonymous Poster
#5

Re: Unbalanced Load

05/10/2007 5:42 AM

To my understanding a three-phase balanced system is that the phasor sum of the three line or phase voltages is zero, and the phasor sum of the three line or phase currents is zero.

Since you mention neutral, I assume you mean a Y connected system. The sum of the three phases PLUS neutral current add up to zero at every instant. Assuming your supply maintains a constant phase voltage for each phase with respect to neutral, the neutral will have current which is caused by the load imbalance.

Register to Reply
Commentator

Join Date: Feb 2007
Posts: 60
#6

Re: Unbalanced Load

05/10/2007 8:02 AM

In fact, unbalance will cause a negative sequence current.

This will occur in many conditions:

-when a conductor is broken and you are feeding a balanced load, such as a motor

-when a double phase fault occurs

-when a double phase to ground fault occurs

-when a single line to ground fault occurs

For such conditions the best way is to draw the symmetrical components sequence equivalent for the systems and it will be clear in what conditions this happens.

Regards

elbf2801

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Ron Nombri Engineering Fields - Energy Engineering - Ron Nombri Engineering Fields - Power Engineering - Eternal Power Papua New Guinea - Member - Ron Nombri

Join Date: May 2007
Location: Papua New Guinea
Posts: 174
Good Answers: 3
#9
In reply to #6

Re: Unbalanced Load

05/30/2007 5:13 AM

elbf2801,

I agree. Where you will be able to determine your Positive Sequence Components, Negative Sequence Components, and Zero Sequence Components with respect to the unbalance (fault) condition.

__________________
Kind regards, Ron
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#7

Re: Unbalanced Load

05/11/2007 8:24 AM

Your last sentence in the first paragraph: "The imbalance occurs when an open or short circuit appears at the load," isn't quite consistent with your previous statements, even though the last sentence is true as well as the previous statements.

It is very common to have imbalances in a 3 phase panel because all single phase loads aren't the same yet are distributed somewhat evenly among the phases, and I have recently run across a panel which fed a computer lab, lighting, and convenience outlets, which was so unbalanced that it didn't make sense. As it turned out, the transformer feeding the lab was undersized, and had been used for so long, that the transformer started breaking down. When a panel is fed by a poor ol' broken down transformer, it may be impossible to balance the loads, so we swapped it for a larger, younger model.

How would you like to have my experiences expressed?

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#8

Re: Unbalanced Load

05/11/2007 10:32 AM

In a normal delta star connected step down distribution transformers the balancing of load in each phase is a very difficult task when loading is combination of three phase power and single phase power and lighting loads.Hence the phase currents will not be uniform causing neutral shift .For a domestic power distribution lines the single phase loading is so uneven that there will always be unbalanced loading resulting large voltage variation in phase voltage and if the neutral earthing is not absolute there will exist neutral floating voltage which is harmful to electronic equipment. While designing LT distribution lines lot of care to be taken to balance the single phase loads. It is always better to use isolation transformers/ constant voltage transformers for computers and computerised controlled equipments in unbalanced loading systems.

Register to Reply
Register to Reply 9 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Bill (1); elbf2801 (1); jack of all trades (1); Ron Nombri (1); techno (1); V (1); V.I.Abraham (1)

Previous in Forum: Looking for a way to do the following....   Next in Forum: Programming Language : Undergraduate Electrical Engineer
You might be interested in: Line-shaft Spools, Power Line Network Components

Advertisement