Surge Vessel Precharge Pressure

04/26/2012 3:51 AM

Hi guys,

We have running water supply project in GCC included 6 pump stations and 6 nos surge vessel bladder type. Further to surge designer report the pre-charge pressure should be 7.5 bar, 17 bar, 22, 24, and 30 bar.

Is there any limitation for precharge pressure and why?

How to reduce this pressure?

Regards

Ali

Register to Reply
Pathfinder Tags: surge vessel
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Surge vessel precharge pressure

04/26/2012 3:55 AM

<...GCC...>

Wha'?

<...Is there any limitation for precharge pressure and why?...>

The structural design of the vessels?

<...How to reduce this pressure?...>

Bleed some of the precharge from them?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#2

Re: Surge vessel precharge pressure

04/26/2012 4:17 AM

Are each station working at a different pressure?. What are the required pressure of each station including pump start/stop(cut in/cut off) pressure?. Are the rubber bladders and tanks rated for those pressures?.

__________________
pnaban
Register to Reply
Power-User

Join Date: Oct 2009
Location: Central Midwest
Posts: 455
Good Answers: 38
#3

Re: Surge vessel precharge pressure

04/26/2012 7:31 AM

What did the vendor recommend when you contacted them ?

__________________
We have met the enemy....and he is us. POGO
Register to Reply
Guru
Popular Science - Cosmology - New Member Engineering Fields - Civil Engineering - New Member Engineering Fields - Nuclear Engineering - New Member United States - Member - New Member

Join Date: Aug 2010
Posts: 714
Good Answers: 38
#4

Re: Surge Vessel Precharge Pressure

04/26/2012 11:20 AM

I've only done a handful of surge tank designs, but a 30 bar preload surprised me. I'm curious, what type of water supply application is this?

__________________
Sometimes my thoughts are in a degree of order so high even I don't get it...
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#5

Re: Surge Vessel Precharge Pressure

04/26/2012 3:39 PM

Precharge pressure depends on the working pressure of the system. Normally precharge to ~ 1/2 the absolute working pressure. Then when the surge vessel sees system pressure the air compresses to 1/2 the vessel volume and you have 1/2 water, 1/2 air in the vessel, usually about right to handle higher and lower pressure fluctuations.

__________________
Give masochists a fair crack of the whip
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #5

Re: Surge Vessel Precharge Pressure

04/26/2012 10:56 PM

Does it(air pressure) have any relationship to the cut-in pressure?. We charge with nitrogen instead of air as air in contact with moisture will corrode the interior of the vessel.

__________________
pnaban
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#8
In reply to #7

Re: Surge Vessel Precharge Pressure

04/27/2012 11:13 AM

Yes, you want the cut-in pressure to be above the pre-charge pressure. Then as the system pressure slowly falls, the pump restarts before all the water has left the vessel. If the cut-in pressure is lower, when all the water has left the vessel the pressure falls rapidly to cut-in point, and when the pump starts there is no surge protection till pre-charge pressure is reached, potentially causing water hammer.

__________________
Give masochists a fair crack of the whip
Register to Reply
Commentator

Join Date: Nov 2009
Posts: 78
Good Answers: 9
#6

Re: Surge Vessel Precharge Pressure

04/26/2012 10:52 PM

Hi Ali

1. The initial pressure would depends on the final volume of air that you want it to be in the surge vessel. You can use following equation

Po = P x (V/Vo)

where, Po is the initial pressure, P is the normal operating pressure V stands for volume of air and V/Vo is the ratio of final volume to that initial volume of air inside the surge vessel. Vo = volume of surge vessel.

2. Let say if you want the air final volume to be 1/2 of initial volume (V/Vo = 0.5) than Po = 0.5P. If the final volume is 1/4 (V/Vo = 0.25, water 3/4 full) then Po = 0.25P

3. The above equation is derived from the universal gas law PV=nRT. Since nRT are all constants, pressure is a function of volume only.

Register to Reply
Participant

Join Date: Apr 2012
Posts: 2
#9

Re: Surge Vessel Precharge Pressure

04/30/2012 11:34 AM

Project water supply to top of mountain including 5 nos pump station with 2+1 high pressure pumps with FLOW 52 LPS as below Head. DI pipe line by length of almost 21 km

1- no.1 pump station Head 174 mtr

2- 351 mtr

3- 348

4- 411

5- 356

ali

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ali 47 (1); ChaoticIntellect (1); Codemaster (2); MJCronin (1); pnaban (2); PWSlack (1); sabriahmad (1)