European Motor Use in Asia

04/26/2012 11:59 PM

I have a European Standard Induction Motor as rated :

Volt : 380 Vac

Freq: 50Hz

Output: 22kW

Rpm: 1480rpm (4 pole)

In Asia, 3Phase power requirement will be: 415V, 50Hz.

I would like to use this motor in Asia. In my opinion, considering the voltage drop along the line from MCC will reduce the volt to some varies value. Does the value would make the motor run?? Is it run efficiently?? Any other things that we should consider??

__________________
Elect & Instr
Register to Reply
Pathfinder Tags: motor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: European Motor Use in Asia

04/27/2012 1:10 AM

You will have to save the image and blow it up in size.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 3)
Participant

Join Date: Apr 2011
Location: Syria - Aleppo city
Posts: 4
#2

Re: European Motor Use in Asia

04/28/2012 12:30 AM

Alsalamo Alaykom Dear,

You can use VSD directly without any modification

Eng.Ihsan

Register to Reply Score 1 for Off Topic
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#3

Re: European Motor Use in Asia

04/28/2012 10:28 AM

TonyS response sums it all. It can be said that the three phase, 50Hz motors rated 380V, 400V, 415V, 440V can be interchangeably used without any problem to the motor.

The torque and current characteristics change depending on the actual voltage vis-a-vis the rated voltage and that needs to be verified with the connected load requirements and the switchgear component ratings.

__________________
Raghunath
Register to Reply
Guru
Hobbies - Musician - New Member United Kingdom - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Transportation Engineering - New Member

Join Date: Mar 2007
Location: England
Posts: 951
Good Answers: 48
#4

Re: European Motor Use in Asia

04/28/2012 4:54 PM

Until about 15 years ago European 3ph motors were 380v and UK motors 415v, then they decided to standardise at 400v. In reality not a lot was changed, and these motors will usually easily run at 400v plus or minus 10%, so you should be OK.

Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Eng.Ihsan (1); Holzfeller (1); raghun (1); TonyS (1)

Previous in Forum: Cable Fault Location   Next in Forum: Surge Passing Through a Double Conversion Type UPS

Advertisement