Anonymous Poster #1

Surge Passing Through a Double Conversion Type UPS

04/27/2012 5:02 AM

1/ Is there any chance a Switching/ lightning surge occured in the upstream of UPS, passing upto the load via an on line double conversion type (transformer less) UPS.

2/ Some suppliers says, in this ups the neutral and earth is internally not disconnected, and therefore this can happen. is it true???.

3/ What could be done to prevent this???.

Thank You!

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: SURGE PASSIJING THROUGH A DOUBLE CONVERSION TYPE UPS

04/27/2012 5:05 AM

A3: fit lightning protection to the premises according to current local standards. It will not prevent absolutely any damage, though it will minimise the risk.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Member

Join Date: Apr 2012
Posts: 5
#2
In reply to #1

Re: SURGE PASSIJING THROUGH A DOUBLE CONVERSION TYPE UPS

04/27/2012 6:59 AM

Thaks for your reply.

Does it sense that, theere is a possibility in passing a surge hrough double conv. online UPS??????

Thanks!

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: SURGE PASSIJING THROUGH A DOUBLE CONVERSION TYPE UPS

04/27/2012 7:30 AM

Others may answer the other two questions. Be patient!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#4

Re: Surge Passing Through a Double Conversion Type UPS

04/27/2012 8:29 AM

A lightning surge can be present on one or both conductors to the UPS. Unless it has an internal short to earth, it should not be affected when the lightning is present on both conductors.

If the lightning is present on just one conductor it is possible to disable the UPS entirely. So, a good surge protector that uses metal oxide varistors helps as long as they are located very close to the conductors providing power. In other words, do not hang them as an accessory on some long wire.

The more MOV's the better. Each one is capable of a couple thousand Ampers for a short time (as in a lightning strike). Several in parallel provides extra capacity and assurance that some have survived after the incident. Don't worry about the number of joules they advertise for capacity. Instead, look at the total peak amps they can bypass and at what level they kick in. A protection level on 20,000 Amps peak is a good starting point.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#5

Re: Surge Passing Through a Double Conversion Type UPS

04/27/2012 11:44 AM

1/Yes

2/Yes. If the UPS has neutral bonded through and the UPS is therefore not a separately derived service, then definitely. However, even UPS' configured as separate services would be susceptible through the transformers and the grounding conductor (potential rise).

3/Joe has posted a good idea. Here is a good paper from Littelfuse on the subject.

Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#6

Re: Surge Passing Through a Double Conversion Type UPS

04/27/2012 11:38 PM

Yeah, all the guys replied something useful, but.....

The double conversion UPS - AC-DC-AC - is conceived to prevent this and similar problems. I had a few - well designed ones - operating over decades without fail.

BUT, both design and maintenance have to know, and take into account, at least of the basics. If you place the batteries - for structural reasons on the other side of the building, how much of inductance is introduced, that nobody asked for? Maintenance did maintain the low ohm connections?

Unless such questions are handled properly, lesser issues are of no importance.

Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#7
In reply to #6

Re: Surge Passing Through a Double Conversion Type UPS

04/30/2012 12:40 PM

Hopefully all of your DC cables are properly shielded through properly bonded conduit, shortest runs feasible, routing, etc. and those circuits would therefore not be able to introduce the effects of a lightning strike through the inverter portion of the UPS.

Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#8
In reply to #7

Re: Surge Passing Through a Double Conversion Type UPS

04/30/2012 12:53 PM

While your opinion is valid, That is emphatically not the point. Original designs assume, for example no induction in the leads to the battery, not any induction in the construction of the batteries themselves.

On the other hand, dI/dt limits the dampening effect a battery set can exert. Long cable = poor dampening. That's it.

Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#9
In reply to #8

Re: Surge Passing Through a Double Conversion Type UPS

04/30/2012 4:50 PM

I thought the OP's question was about switching/lightning surges to the inverter portion of the UPS:

1/ Is there any chance a Switching/ lightning surge occured in the upstream of UPS, passing upto the load via an on line double conversion type (transformer less) UPS.

2/ Some suppliers says, in this ups the neutral and earth is internally not disconnected, and therefore this can happen. is it true???.

What effect would DC induction have on the neutral of the supply other than the obvious overall loading and inefficiency induced by long cables?

I didn't know we had switched to induction theories from DC.

Reply