Remote I/O or CClink

04/30/2012 10:37 AM

Dear Gurus,

How can I find more info about CClink or Remote I/O ,any specific homepage for reference.

I would like to know how cclink or remote I/O works.How they connect to PLC and how

to write the program to PLC to link with Remote I/O.

Thank you.

Register to Reply
Pathfinder Tags: CClink /Remote I/O
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Remote I/O or CClink

04/30/2012 10:42 AM

Click here, or here.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Member

Join Date: Dec 2010
Location: Los Angeles
Posts: 9
#2
In reply to #1

Re: Remote I/O or CClink

04/30/2012 9:48 PM

Remote IO can be any data collection far from the PLC. For example, you may have five thermocouples on a machine 300 feet from the PLC. One way to read them is by running five thermocouple extension wires from a thermocouple card in your PLC. But this is a lot of expensive TC wire, and subject to a lot of noise pick up. Instead, you can have one twisted pair RS485 serial line running to a remote thermocouple IO module. The protocol running over the serial line could be a common one like Modbus RTU. An example of a remote IO module like this is http://www.icpdas-usa.com/products.php?PID=480 which has 8 input channels (three extra).

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Remote I/O or CClink

05/04/2012 8:23 PM

As a concept, "remote I/O" is just what it says, any form of I/O equipment that is not directly attached to whatever your process controller is, a PLC, DCS, PC etc. etc. So when used as a generic term, it can mean anything and the way the processor communicates to it can be anything.

CC-Link is a communications protocol, one that would be USED by remote I/O to talk to a processor somewhere. it's a specific form of what is generically called a "fieldbus". Fieldbus systems can be EtherNet, DeviceNet, ControlNet, Hart Interface, Modbus, Modbus+, Profibus, Sercos, all kinds of different protocols exist, mostly promoted as "open" standards, but generally pushed by one or two vendors over the others so as to try to lock end users into their platform. For example DeviceNet was pushed initially by Allen Bradley, Profibus by Siemens, Modbus by Schneider (ex Modicon), Hart by Rosemount, and CC-Link is now being pushed mainly by Japanese companies like Mitsubishi and Idec.

However, "Remote I/O" (big R) was at one time a SPECIFIC form of internal communications protocol for Allen Bradley PLC-5 Series PLCs. It was how a CPU communicated to any I/O rack that was not physically attached to it. RIO was sometimes referred to a "Blue Hose" because the cable used by A-B was always blue. Because of the ubiquitous nature of A-B PLCs in North America, a lot of 3rd party vendors (of things that A-B did NOT make themselves) came up with Remote I/O interfaces for their products, and instrumentation was something that A-B did not get into, so there are a lot of instrumentation vendors that still offer "Remote I/O" interfaces for their products. A good rule-of-thumb is that if the vendor capitalizes it, as in "Remote I/O" instead of "remote I/O", then they are likely referring to the specific A-B interface protocol, not the generic use as external I/O for anything.

But even A-B hardly ever uses Remote I/O any longer, they switched to DeviceNet, ControlNet and most recently EtherNet for remote (small r) I/O communications. If you are looking at deciding on "big R" products, I wouldn't.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Register to Reply 3 comments