Flowrate Control with VFD and Electropnuematic Control Valve

04/29/2012 9:45 AM

Hi,

I would like to control flowrate for water through a vfd governed by a PID (ratio controller) as well as controlling v/v also governed by the same PID. The pump is multistage centrifugal and the flowrate that I would want to maintain is in the range of (15-45 lit/hr). The issue I am facing is that massive hysterisis and set point is achieved after a long delay while using all three of the following options

1. controlling the flowrate only with flow valve.

2. controlling it with VFD.

3. controlling it with both VFD and flow valve.

Please advise if its possible that I can use the internal speed correction PID mechanism of VFD along with the mAmps injected into it from the ratio PID controller.

Any other helpful tips would also be appreciated.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Flowrate control with VFD and electropnuematic control valve

04/29/2012 1:55 PM

The flow rate seems very low for use with a centrifugal pump. In order to meet the head requirement, the pump may need to run at a substantial fraction of full speed, in which case the flow may be excessive. This could result in the high hysteresis.

If the pump is reasonably matched to the desired flow rate, I think your option of PID controller interfaced to VFD would be best.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Apr 2012
Posts: 5
#4
In reply to #1

Re: Flowrate control with VFD and electropnuematic control valve

04/30/2012 12:15 AM

If I am only using VFD with PID controller, then the issue I am facing are

1. Once the flow requirement is 15 lit/hr then the motor is running at very low frequency around 5 Hz, my concern is that if I go onto implement this motors bearings might wear down or related issues might come up

2. Secondly, during the process of achieving set point if the PID controller send command signal (say 4mAmps) to the drive, it shuts off the motor getting the flow back to zero and then starts it as command signal (mAmps) goes higher. Thus the SP is not achieved.

3. To counter the scenario in '2' I am keeping the lowest frequency of drive to 5Hz for min command signal of PID i.e. 4mAmps still massive hysteriss observed.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: Flowrate control with VFD and electropnuematic control valve

04/30/2012 12:23 AM

This suggests that the pump is the wrong type, or way too oversized, for the application.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Member

Join Date: Apr 2012
Posts: 5
#8
In reply to #5

Re: Flowrate control with VFD and electropnuematic control valve

04/30/2012 12:36 AM

I do agree and was to an extent aware of this fact but unfortunately I would have to live with it. The customer won't be willing to spend extra bux.

Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#2

Re: Flowrate Control with VFD and Electropnuematic Control Valve

04/29/2012 3:50 PM

1) Can you control the loop in manual? 2) Do you have a flowmeter with an electronic output?

Register to Reply
Member

Join Date: Apr 2012
Posts: 5
#6
In reply to #2

Re: Flowrate Control with VFD and Electropnuematic Control Valve

04/30/2012 12:23 AM

1. Yes the loop can be controlled manually via PID controllers interface.

2. Yes the flowmeter with electronic output is present, upon the PV provided by this flow meter the PID controller regulates the flow.

PID controller type: Siemens SPIRAT20.

Flowmeter: KOBOLD variable area

Register to Reply
2
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#3

Re: Flowrate Control with VFD and Electropnuematic Control Valve

04/29/2012 5:59 PM

If it was me I would just feed the pumps output through a fixed nozzle or restrictor and adjust the output pressure of the pump up or down according to how much flow rate I needed using the VFD unit and a pressure sensor for feedback.

Using two variable units, onr pressure based and one flow based, in one system to get one specific flow rate seems like pointless design overkill. Use one or use the other but not both.

Register to Reply Good Answer (Score 2)
Member

Join Date: Apr 2012
Posts: 5
#7
In reply to #3

Re: Flowrate Control with VFD and Electropnuematic Control Valve

04/30/2012 12:33 AM

I am actually looking for high precision as the flowrate of water is critical for the fuel purification in this scenario.

Well, currently I don't have anything for pressure sensing I am just doing test runs for controlling VFD (SAMCO) and SAMPSON's electropnuematic valve via PID(Siemens SPIRAT20) whose sensing is based on flow rate sent by KOBOLD variable area flowmeter.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #7

Re: Flowrate Control with VFD and Electropnuematic Control Valve

04/30/2012 4:28 AM

Variable Area is not a "high precision" technique!

+/-5% is typical.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: Flowrate Control with VFD and Electropnuematic Control Valve

04/30/2012 4:32 AM

Go for a fixed setting for the pump and vary the flowrate through some sort of small aperture actuated valve with PI control on the flowmeter's signal to achieve the desired set flow. Derivative control is not needed and the integral setting will be slight.

Some method of getting rid of the surplus flow is needed so as to keep the pump happy. How about a pressure sustaining valve downstream of the controlled flow take-off and sending the surplus liquid back to the day tank?

Don't use cost as an argument. Go for the best technical approach.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#11

Re: Flowrate Control with VFD and Electropnuematic Control Valve

04/30/2012 10:00 AM

Based on your statements regarding obviously oversized pump, your best choice- for both flow control and pump life- is to abandon the VFD and use only a flow control valve (sized appropriately for the desired flow) and install a pressure-activated by-pass valve to recirculate MOST of the flow back through the pump.

This assumes that the pump heating due to efficiency issues is not a problem. If that could be an issue, use the VFD but set it at a fixed level, maybe 25% of maximum flow, and still use the flow control/by-pass valve assembly.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#12

Re: Flow rate Control with VFD and Electropnuematic Control Valve

04/30/2012 10:44 AM

If you are looking for high precision batch metering capabilities you are using the wrong pump and control methods all together.

You need a properly sized positive displacement pump system not a multistage centrifugal one.

Register to Reply Good Answer (Score 2)
Power-User

Join Date: Oct 2010
Location: Base in Madrid, Spain. Updated location every several months.
Posts: 126
Good Answers: 3
#13

Re: Flowrate Control with VFD and Electropnuematic Control Valve

05/01/2012 7:10 PM

If vfd control takes it to 5%...

Could you post the specifications of the pump you have?

If change of pump is not an option, I agree that recirculation to tank seems the better way.

Salu2 cordiales.

__________________
Everyday learning.
Register to Reply Score 1 for Good Answer
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

abelmh (1); dehammad (4); energygod (1); Iris (1); PWSlack (2); tcmtech (2); Tornado (2)

Previous in Forum: Level Transmitter Use as Flow Measurement   Next in Forum: Remote I/O or CClink

Advertisement