REF Protection for Transformer

05/26/2012 2:34 AM

Dear experts,

my query is what is the need of REF protection for transformer when we are having differential protection.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#1

Re: REF Protection for Transformer

05/26/2012 9:53 AM

A Restricted Earth Fault (REF) protection is required to protect the transformer from earth fault of a restricted/localized zone of a circuit and are more sensitive.

An REF relay works by measuring the actual current flowing to earth from the frame of the unit. If that current exceeds a certain preset maximum value of milliamps (mA) then the relay will trip to cut off the power supply to the unit.

Differential protection relay operate by sensing the in balance of the windings of a transformer . REF protection is added to transformers in order to detect ground faults on a given winding more sensitively than differential protection relays.

The following link will give detailed information about transformer protection.

http://www.basler.com/downloads/transfguide.pdf

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: REF Protection for Transformer

05/27/2012 7:35 AM

Good Question! But, because of the high bias setting in the differential relay, say, of the order of 10 to 20%, you need 10 to 20% of earth fault current for the diffrential relay to respond to an internal earthfault in the trf. This is particularly problematic, if the trf. neutral is impeadnace earthed and the eath fault in the winding is close to the neutral. In such situations REF relays defilnitely help, as they are more sensitive.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2012
Posts: 22
#3

Re: REF Protection for Transformer

06/07/2012 1:53 PM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Register to Reply Off Topic (Score 5)
Register to Reply 3 comments