PC Restart Problem During Changing-Over of UPS

05/26/2012 5:11 AM

Dears,

I have a Line-Reactive UPS 1000VA on which a fan, a light and a PC run. I have a problem that when I switch off the breaker of utility incoming power to UPS, I don't face PC restart problem but when utility power goes off (for whole town), PC restarts. Can anybody guess what could be the reason?

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#1

Re: PC restart problem during changing-over of UPS

05/26/2012 8:09 AM

Maybe you should call the manufacture of the UPS on this one.

The only thing I can think of is the voltage decay rate is going to be different from a breaker tripping to the mains dropping out.

I suspect that the mains will not drop as rapidly and the trip point where the UPS kicks in is too low to prevent the PC from going into shutdown.

I would also recommend a separate UPS for the fan (if you must), as that is an inductive load.

Register to Reply Good Answer (Score 2)
5
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: PC Restart Problem During Changing-Over of UPS

05/26/2012 11:41 AM

"Whole town" blackouts are often preceded by a "brown out" in which theline (mains) voltage dips precipitously. During that condition, your fan motor is drawing more current but turning slower. When the power does finally fail and the UPS switches over, the fan connects out of phase with the line power from the UPS, which likely goes into current limit to protect itself. That probably causes your PC power supply to shut down to protect ITself.

Having a fan, or anything with an AC motor, on a UPS is never adviseable if the primary purpose of the UPS is to keep a PC operating. Separate the fan on another UPS if it is so important.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 5)
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1205
Good Answers: 54
#6
In reply to #2

Re: PC Restart Problem During Changing-Over of UPS

05/27/2012 10:09 AM

Don't put resistive loads on them either. That means Laser printers (fuser) and floor heaters. I see both all the time and it's no mystery the UPS can't handle it!

__________________
Most people are mostly good most of the time.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #6

Re: PC Restart Problem During Changing-Over of UPS

05/27/2012 10:42 AM

Lol, yes I've seen under-desk heater plugged into the UPS, then people wonder why in only lasts a minute or two! I once saw a 1500W heater plugged into a 500W UPS, it was as if the UPS wasn't even there.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#8
In reply to #6

Re: PC Restart Problem During Changing-Over of UPS

05/27/2012 7:43 PM

Yes Laser printers.

I have seen special notes for Laser printers in the UPS Catalogues whether it can handle or not.

Register to Reply
Power-User

Join Date: May 2007
Location: Ronan, Montana
Posts: 174
Good Answers: 10
#3

Re: PC Restart Problem During Changing-Over of UPS

05/27/2012 12:57 AM

The bios of some motherboards have a feature which will restart the system after a power outage. This is probably what is happening to yours.

To expand the thought just a little, some people want their computers to restart after a power outage. So here's how to do it, if your computer doesn't have the bios feature. (This was posted on Tom's Hardware by Chris Priede) There is no sense restating something clearly detailed.

You can make it "always on" by grounding the pin 14 of the ATX power supply. The wire going to pin 14 is usually green. Cut it a couple inches from the motherboard's
power connector (so that it can be reconnected if needed). Strip off some
insulation from one the (usually black) wires going to the adjacent pins 13,
15 - 17 without severing the wire itself; connect the power supply end of
the green wire to it. Leave the motherboard end of the green wire open.

__________________
"don't be so open minded that your brain falls out" unknown
Register to Reply
Power-User

Join Date: Sep 2011
Posts: 267
Good Answers: 7
#4

Re: PC Restart Problem During Changing-Over of UPS

05/27/2012 1:06 AM

I'm wondering if it could be frequency related. Just suppose that the frequency changes, will the UPS behave?

I'd call the manufacturer. You could also rent a power line disturbance monitor and find out what really happens when the utility goes down. You could also have regeneration within your plant or subsystem from motors continuing to spin.

You could try cutting power to the building.

Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#5

Re: PC Restart Problem During Changing-Over of UPS

05/27/2012 4:44 AM

Regard.

Answer in post #1 seems more logical as the behaviour of UPS on manual-switching is OK but on disturbance in power line can not be handled on Blackouts by UPS as one of the reason given in post #2; i.e. brown-out before black-out.

And I add that jerks/spikes in power line are a major cause of power failures due to heavy inductive load changes causing hi-surges/spikes.

Register to Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#9

Re: PC Restart Problem During Changing-Over of UPS

05/28/2012 1:32 AM

You did not mention this problem is there since beginning of UPS installation or this problem started over a period of time?

  1. If there is a switch on your UPS back side to select Inverter/ UPS modes change the switch to UPS mode. May it is in inverter mode. Then you will start hear a beep sound at regular time intervals.
  2. Open your ATX SMPS if you know electronics, check big electrolytic capacitors. Replace if faulty (low micro-farads) or increase capacity by 20%.
  3. Change small changeover relay in your UPS.
__________________
Subramanyam
Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#10

Re: PC Restart Problem During Changing-Over of UPS

05/28/2012 7:54 PM

What model \ brand UPS is it??

Some of the cheaper line-reactive units do Not switch quickly enough <0.1s.

If this is the case, the PC will actually lose power and re-boot.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#11
In reply to #10

Re: PC Restart Problem During Changing-Over of UPS

05/28/2012 9:05 PM

I think the root of the problem is the fan. If it is taken off and the problem goes away, then we know for certain. However, powering an inductive load and a computer on a UPS is not a good idea for reasons already stated.

Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#12
In reply to #11

Re: PC Restart Problem During Changing-Over of UPS

05/29/2012 5:22 PM

Not going to disagree with you, while I think it (the fan) is the most likely cause, I wont discount battery age and condition or the type of UPS he/she is using either.

If it has been working previously and is only now exhibiting the issue described above, other issues could be coming into play.

However, if it is a brand new UPS, then the fan is likely the only cause.

Those small UPSs are only really designed to support a PC and Monitor or two long enough to shutdown cleanly.

They should not have heaters, fans, toasters or fishtanks on them... and I've seen all of the above in an office.

My personal favourite is the woman who tried several times to put an electric blanket over her chair to keep warm "cause the AirCon was too cold".

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Power-User

Join Date: May 2007
Location: Ronan, Montana
Posts: 174
Good Answers: 10
#13

Re: PC Restart Problem During Changing-Over of UPS

05/29/2012 6:29 PM

Gentlemen,

While I greatly respect all of your thoughts and wisdom and I know many things cause a computer to act strangely, there is still one thing I do know. A computer will not restart on it's own after a power loss, unless it is enabled in the bios or it's rewired to cause it to restart..

Now, the OP's situation is strange and weird as to what's happening and how it happens but we still can not ignore the bios. OR, perhaps he has a intermittant situation in his connections/ wiring to cause the effect I described in my previous post.

__________________
"don't be so open minded that your brain falls out" unknown
Register to Reply Score 1 for Good Answer
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#14
In reply to #13

Re: PC Restart Problem During Changing-Over of UPS

05/29/2012 10:10 PM

Randyl,

The software that comes with many of the UPSs available have options to restart your machine once the power has returned either WOL or Serial\USB.

If the drivers are installed it can be done. My servers\PCs are all set-up to restart once the power is back & the battery reaches 20% capacity. The UPS also shuts down and restarts each day to cover business hours.

It does depend on how the system is setup and how old the equipment involved is, but the capability has been around for a while.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Power-User

Join Date: May 2007
Location: Ronan, Montana
Posts: 174
Good Answers: 10
#15
In reply to #14

Re: PC Restart Problem During Changing-Over of UPS

05/30/2012 12:21 AM

Sapper,

You're right! It's been a few years since I retired. I must be getting a little old and fuzzy.

Randy

__________________
"don't be so open minded that your brain falls out" unknown
Register to Reply
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#16
In reply to #15

Re: PC Restart Problem During Changing-Over of UPS

05/30/2012 7:34 AM

Thanks to all participants.

I have understood that the problem is "brown out before black out" not the that the fan is also running on single UPS with PC. If fan is also a problem then when i switch off the incoming mains to UPS, PC should also restart but not. It re-starts when utility goes out.

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#17
In reply to #16

Re: PC Restart Problem During Changing-Over of UPS

05/30/2012 8:04 AM

Maybe. However, you can isolate the problem by taking the fan off the uPS and see if the problem remains or goes away.

If the problem remains, then the issue is with the UPS. Call the UPS manufacture tech support.

If the problem goes away, then you know that the UPS can not drive the inductive load, which is a bad idea as stated before.

When the UPS kicks in there will most likely be a phase shift between the mains AC ad the inverter's AC phase. This can (depending on the phase shift) result in a large back-EMF pulse into the UPS. Not only does this stress the UPS, it will spike at the PC's power supply.

Even if the fan is not the direct cause it still is a bad idea to run the fan from the UPS.

Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#18
In reply to #13

Re: PC Restart Problem During Changing-Over of UPS

05/30/2012 8:14 AM

Regards

Well gentleman please read the post once again.

The complaint is not that PC does not restart but it SHUTs DOWN on Power-outings of a typical condition, while it is running on UPS.

Otherwise you have a valid point for otherwise restart problem.

Register to Reply
2
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#19
In reply to #18

Re: PC Restart Problem During Changing-Over of UPS

05/30/2012 9:08 AM

Reading the post does not clarify what "Restart" really means. You can only guess based on the information given.

However, you can reasonably assume that the system operates normally when the breaker is thrown manually, but operate abnormally when the power is cut to the whole neighborhood.

The next logical question is what is different (from the UPS perspective) between throwing the breaker and an actual blackout?

That answer is probably the rate of decay of the main voltage, which on the breaker side is probably a very steep voltage drop, whereas the actual blackout condition is much slower in decay due to the grid itself acting as a momentary "battery".

The logical conclusion is that the UPS is not responding correctly to a slow voltage decay.

Since the fan is not something you should run with a UPS it isa point of suspicion for me and I would first remove it and see if the UPS functions as it should so as to eliminate any extraneous conditions.

Register to Reply Good Answer (Score 2)
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#20
In reply to #19

Re: PC Restart Problem During Changing-Over of UPS

05/30/2012 5:37 PM

I popped in a GA with this.

The OP needs to undertake a systematic approach to the problem.

The Fan most of us agree should not be on the UPS and is the most likely culprit.

So eliminate the most obvious problem, the fan, then possibly the light as it is extraneous and probably does not need UPS support.

If the issue still present, then it is a UPS related issue, if it is no longer an issue, then the fan is the root cause and the issue is identified.
I can't say resolved as I can't be sure the fan wont be plugged back in.

Regards,
Sapper.

__________________
It's all about the Boom! - MythBusters
Register to Reply
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#21
In reply to #20

Re: PC Restart Problem During Changing-Over of UPS

05/31/2012 6:37 AM

I have checked that even if i remove the fan from UPS, problem doesn't solve. I need to calibrate the UPS to switch on inverter if mains voltage drops at near about 195VAC. I think (not sure) UPS inverter enables at 170V which is the caused by PC to restart.

I am still confused why utility supply first "browns out" then black out. What i understand, when 11KV switches off, the large connected "inductive load" caused an "inductive kick back" which then caused a "brown out" before black out. The charged high tention lines may also be caused by this brown out. Am i right or just a cloddish thought?

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#23
In reply to #21

Re: PC Restart Problem During Changing-Over of UPS

05/31/2012 5:14 PM

If you are getting a lot of these power fluctuations, as well as changing the settings on the UPS to protect yourself.

You need to contact the utility company, because someone on the LV side of the transformer is pulling more power than the Transformer can support, thus the transformer protection is acting to protect the transformer.

As Current Increases, Voltage at the supply will drop, until the overcurrent protection kicks in and causes your voltage drop (Brown out) followed by Breaker Opens (Power Fail) seen at the UPS.

So first protect you system, Change the UPS trigger to 195V AC.
Second, Call the utility and put in a complaint or service request.

Regards,
Sapper.

__________________
It's all about the Boom! - MythBusters
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#22
In reply to #19

Re: PC Restart Problem During Changing-Over of UPS

05/31/2012 6:57 AM

Regards:

<.. decay due to the grid itself acting as a momentary "battery".>

Yes!

I remember a project "How to Store Inductive Energy" or some thing like it in I think 1960s where the purpose was not to loose power on <½ Cycle power outage for critical loads.

Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#24

Re: PC Restart Problem During Changing-Over of UPS

05/31/2012 11:08 PM

Regards.

In Lahore. How frequent the intruptions? I know the situation there.

See if some Welding shop is in your vicinity.

Arc welding generatates very dangerous spikes and brown-outs; locally assembled UPS are not capable of.

Even sophiscated design may kneel before the local power outages and disturbances.

Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#25
In reply to #24

Re: PC Restart Problem During Changing-Over of UPS

06/01/2012 10:55 AM

Wow, what a concept. Welcome to the Third World. Not everybody has the benefit of a strong grid.

I wonder if this situation could be helped by the large capacitor 'power conditioners'? Maybe not for the whole building, but just the sensitive equipment. My larger UPS units have nice big caps, I imagine that is what they are doing, compensating for/absorbing spikes.

__________________
mike k
Register to Reply
Register to Reply 25 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: