Anonymous Poster #1

questions

05/31/2012 2:42 PM

1) why Clean earth and dirty earth are seperated and connected together at last.?

2) what is the resistance between the clean earth wire / dirty earth wire with respect to the common earth rod.?

3) Field instrument cable shields are not connected to the earth in the field junction box. why?

4) Fiels instruments are not connected to earth.why?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: questions

06/01/2012 3:52 AM

A1) So that any current appearing on the dirty earth during a fault event has the least chance of appearing on the instrument earth and affecting the instrumentation readings during that event.

A2) As low as is practicable.

A3) So that circulating currents ("ground loops") are not set up within the instrument cable shields. These currents might otherwise affect instrument readings by inductive interaction between the shields and the signal-carrying conductors in each cables.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Good Answer (Score 2)