Overload vs Short Circuit

06/03/2012 5:16 PM

both overload and short circuit are over currents.regarding motor protection,upto what percentage of overcurrent should be protected by overlod relay and above that by definite time short circuit.is there any relevant standard.i read in an article that upto 250 % of FLA should be protected by inverse time thermal overload and above that by short circuit i.e I>

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Overload vs short circuit

06/03/2012 6:25 PM
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Overload vs Short Circuit

06/04/2012 11:54 AM

As far as I can recall, no standard on protective relays has used the term short circuit with a protection perspective. All they say is only overcurrent. Moreover, these are relative terminologies. For a 1000A feeder, a fault current of 2000A may be just overload but for a 100A feeder, it could be short circuit. There are no clear demarcations. During an actual short circuit between two points at different potential, the short circuit current could be much less than any overload current, if the fault impeadnce is more.

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#3

Re: Overload vs Short Circuit

06/06/2012 7:21 AM

1. Over load setting depend upon the equipment's over load capacity

You may refer IEC standards / manufacturer's rating specs.

Say, Transformers have over load capacity as

10% for 1 Hr. - Over load setting protection

50% for 30 min. - High set current setting of O/L relay

100% for 10 sec. - Instantenous current trip -

(As generally, transformer are with Short circuit capacity of 15-20 times Irated )

__________________
Exploring the Science of Electricity
Register to Reply
Participant
Engineering Fields - Power Engineering - New Member

Join Date: Sep 2012
Posts: 2
#4

Re: Overload vs Short Circuit

09/19/2012 2:58 PM

The overload relay should provide protection upto the breaking current capacity of the contactor and above that SCPD should clear the fault current.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Overload vs Short Circuit

04/26/2023 8:48 AM

This topic is labelled co-ordination. The protocol for doing it can be found in many electrical standards; BS7671 is applicable in the UK.

Overload pertains to the protection of the motor.

Short circuit protection is for the wiring feeding it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6

Re: Overload vs Short Circuit

04/29/2023 2:40 PM

Motor protection it is not a simply explanation. There are standards recommending how to proceed in each country. For instance, in US NEC art.430 [270 of sub articles in about 30 pages] indicates how to fit the protections [see Fig.430.1 attached here].In U.K. BS 7671 ,IEC 60034 and other.

__________________
Julius