Fuse Replacement - Heater Protection

06/05/2012 2:34 AM

Dear sir,

Please help me I have to replace 100A aR 690Volt-700Volt 200kA used for heater protection, the fuse was blown and we have spare 100A gR 690Volt-700Volt 200kA. It is safe or not?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Fuse Replacement - Heater Protection

06/05/2012 4:10 PM

aR and gR indicate Ultra-Rapid response for protecting sensitive semi-conductors.

aR provides short circuit protection while gR provides overload and short circuit protection (effectively a faster response).

Either should be suitable for protecting an industrial resistive heater which generally needs only a slower-responding fuse such as a gL or gG.

__________________
jack of all trades
Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#2

Re: Fuse Replacement - Heater Protection

06/06/2012 2:36 AM

Maybe you would like to find out why it blew in the first place??

__________________
The square root of nothing is what you make it!
Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#3

Re: Fuse Replacement - Heater Protection

06/06/2012 5:41 AM

aR rating is for semiconductor protection while Very very Fast

Fusing elements are so designed to have 3-4 fusing points in series and 2-3 such elements in parallel to ensure max number of fusing points having the highest burn-out probabillity. Pure Silver is used

These are only Short circuit protection. Have very low I² t to cutoff in µS

gR is for Cables and general protection Slugish. I² in mS/S

These are overload protection fusing elements are normally pure copper; but its design is same as aR fuses.

************ Quote ******

  • gR-type: full range protection. Overload and short circuit protection.
  • aR-Type: partial range protection. Short circuit protection only. Faster acting than full range fuses

************ un-Quote ******