Earthing

06/05/2012 3:19 AM

Earthing of shielding is at one point or both side, what is suitable.

Register to Reply
Pathfinder Tags: shielding earth
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#1

Re: Earthing

06/05/2012 10:43 AM

What are you wiring ?

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Earthing

06/05/2012 12:32 PM
Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#3

Re: Earthing

06/06/2012 6:47 AM

It is a common trend to earth the shield of transformer at one point, to eliminate the circulating 3rd harmonics within the shield itself.

But, if it is shielded cable, many belieive to be earthed on one point only, but, I believe that earthing at 2 ends of shield in Shielded cable shall reduce the noise more effective way as compared to that of earthing at one point of shield.

__________________
Exploring the Science of Electricity
Register to Reply