Doubt About Zigzag Earthing Transformers at Site

06/05/2012 7:55 AM

Two zigzag earthing transformers are used for earthing reference to a 33kV Busbar. But, when a generator, connected to that busbar, is on-load, the two zigzag transformers are disconnected from earth because the generator's earthing is used as a reference. However, the zigzag transformers are still online and connected to the 3-phase system but their earthing neutral is the one that is disconnected from earth. Is this a safe practice? will there be any circulating zero sequence currents in the zigzag's winding even if it is not earthed especially in case of high earth faults in the system?
Maybe since there is no path to earth through the zigzag transformer, the zero sequence current may not flow through it. But, I also feel that it will cause problems if the load is unbalanced. Can you people have a say about it from your experience or Knowledge?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2007
Location: ether
Posts: 371
Good Answers: 1
#1

Re: Doubt About Zigzag Earthing Transformers at Site

06/05/2012 10:02 AM

I didn't knew that zigzag transformers had a neutral! Is it a new improvement~?

__________________
“For no man can forbid the spark nor tell whence it may come.” ? Francis Bacon
Register to Reply
Associate

Join Date: Jul 2011
Posts: 29
Good Answers: 2
#3
In reply to #1

Re: Doubt About Zigzag Earthing Transformers at Site

06/05/2012 11:51 AM

I think I made a mistake over there, I didn't mean an actual neutral I meant the point where the 3 phase of the secondary side of the transformer are jointly connected to earth..

Register to Reply
Power-User

Join Date: Jun 2007
Location: ether
Posts: 371
Good Answers: 1
#5
In reply to #3

Re: Doubt About Zigzag Earthing Transformers at Site

06/06/2012 5:03 AM

I think that is a electrical "mass" what you are refering... or the secondary is in star configuration.

__________________
“For no man can forbid the spark nor tell whence it may come.” ? Francis Bacon
Register to Reply
Associate

Join Date: Jul 2011
Posts: 29
Good Answers: 2
#6
In reply to #5

Re: Doubt About Zigzag Earthing Transformers at Site

06/06/2012 5:11 AM

This link shows a picture of how the zigzag earthing transformer is connected:


http://i52.tinypic.com/122m9fq.jpg


You can imagine how it will become if the earth point at the secondary side is removed..

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Doubt About Zigzag Earthing Transformers at Site

06/05/2012 11:32 AM

I don't know about how safe, but wouldn't have thought it the most efficient way of doing it.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Jul 2011
Posts: 29
Good Answers: 2
#4
In reply to #2

Re: Doubt About Zigzag Earthing Transformers at Site

06/05/2012 11:53 AM

I am sure your right, but unfortunately that's the way it is connected.. The zigzag transformers were only added 3 years ago because in the future we will demolish the generator..

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#7

Re: Doubt About Zigzag Earthing Transformers at Site

06/06/2012 7:12 AM

By Principles, you are right.

1. But, We hope for the best, with DG sets, creation of unbalanced voltages is a rare case, as Generator's neutral is always earthed. So, un balanced high voltages on the zig zag transformers will be the very very rare case. Transformer will remain safe during normal operations.

2. But, definitely, Generators will not be prtected by relays connected to zog zag transformers. It will always be for mains breaker only.

__________________
Exploring the Science of Electricity
Register to Reply
Associate

Join Date: Jul 2011
Posts: 29
Good Answers: 2
#8
In reply to #7

Re: Doubt About Zigzag Earthing Transformers at Site

06/06/2012 7:33 AM

I see your point, our generator has its own high resistance earthing and its protection. The zig zag transformer will only be used as a earth reference when the generator is disconnected from the busbar. So I guess as long as unbalanced condition does not exist, the zig zag transformer will remain safe.


What about any harmonics or zero sequence currents flowing in the grid will it be a major concern to the zigzag transformer in this case?

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#9
In reply to #8

Re: Doubt About Zigzag Earthing Transformers at Site

06/06/2012 1:10 PM

Yes, it is safe that way. Earth faults will only be supplied from the generator whose neutral is earthed (there will not be zero sequence currents in the zigzag transformer).

__________________
Raghunath
Register to Reply
Associate

Join Date: Jul 2011
Posts: 29
Good Answers: 2
#10
In reply to #9

Re: Doubt About Zigzag Earthing Transformers at Site

06/06/2012 1:18 PM

Thank you for your clarification..