Two zigzag earthing transformers are used for earthing reference to a 33kV Busbar. But, when a generator, connected to that busbar, is on-load, the two zigzag transformers are disconnected from earth because the generator's earthing is used as a reference. However, the zigzag transformers are still online and connected to the 3-phase system but their earthing neutral is the one that is disconnected from earth. Is this a safe practice? will there be any circulating zero sequence currents in the zigzag's winding even if it is not earthed especially in case of high earth faults in the system?
Maybe since there is no path to earth through the zigzag transformer, the zero sequence current may not flow through it. But, I also feel that it will cause problems if the load is unbalanced. Can you people have a say about it from your experience or Knowledge?