Energy Efficinecy

06/05/2012 8:28 AM

Hi all,

We have eight distribution transformer in our factory.

Two of them is 34,5/0,4 kV and one of them is 34,5/6,3 kV and five of them is 6,3/0,4 kV.

İf we adjust/increase voltage of the low voltage side of transformer from 380 V to 400 V.

Current of motor will decrease %5 percent.

In addition to this we measure the total active power from incoming panel ( from one point ) not from LV side of distribution transformer.

In conslusion if we use 400 V instead of 380 V at LV side ( for motors, pump, ligting etc. ) in our plant will our total active energy decrease % 5.. Is it energy-saving?

Best Regards,

Musa UÇAN

__________________
Unbalance Fault
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#1

Re: Energy Efficinecy

06/05/2012 9:28 AM

only if your paying by the amp. Most of us pay by the watt. P=I*E

380v * 100 amps = 38000 watts

400v * 95 amps = 38000 watts

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Energy Efficiency

06/05/2012 11:48 AM

There is a modest increase in power loss (less efficiency) from insulation leakage currents that will happen by raising the supply voltage. Without knowing what intelligent power supplies or variable frequency drives you have for these unspecified motors, it is impossible to say if this will be more efficient, less efficient or just making your equipment more susceptible to catastrophic failure from a positive power surge.

I think that you should change this transformer wiring to the higher voltage. There's several electricians waiting for your call to repair your facility.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#3

Re: Energy Efficinecy

06/06/2012 12:46 AM

The secondary voltage you are referring to is the open circuit voltage. When the transformer will be loaded fully , 400V will get reduced to approximately 380V due to voltage regulation of transformer. If the % regulation of transformer is 5% then the secondary voltage (x ) at full load will be as under:

5= (400-x) *100 /x i.e. 105 x = 40000 or x = 380.95 V

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#4

Re: Energy Efficinecy

06/06/2012 1:15 AM

When you increase voltage above "standard", you begin to "kill" your electronic lamp ballasts- life will diminish by about the square of difference. So, at 110% of normal, ballast life will be 1/(1.1x1.1) or about 80%- 12 years instead of 15.

Also- motor failure triggered by an occasional voltage spike causing phase-phase failure in winding through insulation. Maybe 10% higher losses- up to 20% with high-effic motors due to thinner insulation and more copper.

Your electronic controls will also be at higher risk of spike failure.

Secondary transformers will not be able to handle rated power flow because their cores get "loaded" by the higher voltage input.

Bottom line- it is not worth it. You may not see it directly, but you WILL be losing money. A site we visited several years ago, with the same thought process, was losing over US$100,000 a year due to this issue. They re-tapped the transformers.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#5

Re: Energy Efficinecy

06/06/2012 6:42 AM

You have mentioned the word 'active energy' & told that the current is reduced by 5%.

Current is not the active energy.

Infact, if you accurately measure the active energy in KWH unit, you will find something different.

On reducing the voltage by 5%, you will find the reduction in motor losses ( magnetic losses & Copper losses ) check the loss curve of motor given by manufacturer

__________________
Exploring the Science of Electricity
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#6
In reply to #5

Re: Energy Efficinecy

06/07/2012 12:16 AM

I agree with you that core loss or magnetic loss will get reduced if the voltage is less. But current will correspondingly increase as Power = √3 V I Cos ø. Hence copper loss will be more.

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#8
In reply to #6

Re: Energy Efficinecy

06/07/2012 7:56 AM

That all depend upon the nature of load.

He has mentioned for Pumps. - Contant head - so, constant power out put - so, current will also reduce little . This can be verified practically - or verified with the head /power curve of pump + loss/voltage curve of motor.

In fact, I had verified the reduction in losses with voltage on shop floor.

__________________
Exploring the Science of Electricity
Register to Reply
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#7

Re: Energy Efficinecy

06/07/2012 4:26 AM

Instead of acting on the voltage level , which itself is not, as said by others, a good solution, you should investigate (amongst others) :

Proper lighting management and may be lighting automation

Installation of VSD to optimize motors usage

Installation of Power Factor Correction and harmonics filtering to optimize losses and tariffs .

But energy efficiency methods is a vast topic, which cannot be adressed in a simple post reply. My advise is to consult some specialist blogs, forums, or manufacturers websites.

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers: