60 Hz VFD on 50 Hz Service

06/05/2012 2:33 PM

Can a 60 Htz VFD be operated on 50 Htz power, or visa versa? I want to use 60 htz motors with a VFD and be able to ship them to a 50 Htz 380v country. The application is centrifugal pump motors. I know I would have to size the HP and impeller for the slower (50) htz speed, no issue there. I know you can overspeed/ underspeed the drive. So I should be able to duplicate pump performance at either Htz rating. the big question is; does the drive have to be rated at 60 Htz and stepped down to 50 htz power, or can it just be ran at 50 htz power?

Joe T

__________________
Inga Binga Bunga Banga Boonga Binga Buuuunnnnga
Register to Reply
Pathfinder Tags: 50/60 Htz VFD Operation
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: 60 Htz VFD on 50 Htz Service

06/05/2012 3:18 PM

"Can a 60 Htz VFD be operated on 50 Htz power, or visa versa? "

Yes and Yes. A VFD doesn't know or care what the incoming line frequency is, all it does is convert it to DC anyway.

But one thing a VFD cannot do is create voltage from thin air. So depending on the operating voltage, you may not be able to make your pumps match performance. at full speed. For example if you are designed around 480V 60Hz, you will only have 400V 50Hz available elsewhere in the world. So although you can turn the sppeed up to 60Hz, you will not be able to give the motor more than 400V at 60Hz. So the V/Hz ratio will be incorrect for your motor and you will lose torque, about 30% less torque than at 480V 60Hz. So unless your motor is over sized by 30%, you wiill over load it.

What you could do is to design your pump to run at 400V 50Hz and use the VFD to turn it DOWN to that if you have 480V available, that way it is universally acceptable everywhere.

If this is for 230V 50 or 60Hz, no problem at all.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Power-User

Join Date: Sep 2011
Location: Near the New Madrid Fault. USA
Posts: 269
Good Answers: 1
#7
In reply to #1

Re: 60 Htz VFD on 50 Htz Service

06/06/2012 9:59 AM

Right on the money again JRaef, had to GA you for that.

__________________
It's not Rocket Science
Register to Reply Off Topic (Score 5)
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#2

Re: 60 Hz VFD on 50 Hz Service

06/05/2012 5:43 PM

I concur with previous comments but wish to add a cautionary note.

I have encountered a situation where motor/pump combination was run in the +/- 10% voltage range and all seemed good UNTIL motors started burning out. (The VFD was being used to vary the motor speed and on occasion was running at faster than design frequency)

The overload protection became ineffective, since overload current at "normal" was not exceeded at the higher supply voltage, all seemed well. Further investigation determined that running continuous duty for extended periods at that condition led to excessive heating in the coils/iron and eventual motor failure.

If you operate at a different frequency, check that the new operating conditions have appropriate modification of the protection circuits.

__________________
Just an Engineer from the land down under.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: 60 Hz VFD on 50 Hz Service

06/05/2012 10:23 PM

Just an Eng makes a good point.... Filters can be used to limit voltage, but there is no substitute for good engineering...

"There are basically three different types of commercially available filter networks for reducing the overvoltages at the motor terminals. These filters are typically installed at the output of the VFD. Line reactors (inductors), resistor-capacitor (R-C) snubbers, and R-L-C low-pass filters are commonly used to reduce the voltage at the motor terminals. In the majority of cases, the R-L-C low-pass filter has been found to be the most effective filter. However, the user should consult the VFD vendor to select the filter that will match the specific VFD that is selected for the application."

"Use of 230 V / 460 V Motors

Many motors are designed for operation from either a 230 V or a 460 V supply. In such cases, 230 V VFDs and motors rated 230 V / 460 V will solve the problem. This is because the insulation systems for dual-wound motors are designed for 600 V rms operation; when 230 V is used, then even if voltage magnification occurs at the motor terminals, the peak voltage is still below the insulation withstand capability of the motor. This is a viable option for many small fractional horsepower motors that have the provision for either 460 V or 230 V operation."

http://www.pge.com/includes/docs/pdfs/mybusiness/customerservice/energystatus/powerquality/vfd_motors.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#4

Re: 60 Hz VFD on 50 Hz Service

06/06/2012 3:02 AM

As stated a VFD does not care about the incoming Hz, as for running your pump with the same performance.

Pump performance depends on efficiency and Hz or RPM, to find out what that is you need to study the pump curve and then what the rate of flow is at your new Hz. To work out what your flow rate would be you need to apply the "laws of affinity". (Google it).

you have two options regarding the voltage.

1. run your motor at the output voltage of your drive, that might decrease the motor HP, (you've not mentioned the drive output voltage or motor NPV) and means you MAY not be able to use a pump with the same number of stages.

2. get yourself a step-up transformer

find the formulas regarding voltage/Hz change & the "Laws of affinity". they should help you.

__________________
The square root of nothing is what you make it!
Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#5

Re: 60 Hz VFD on 50 Hz Service

06/06/2012 5:29 AM

Will there be no problem with the DC voltage ripple on the DC bus in the VFD.

It takes more time in a 50Hz system to reload the DC bus capacitor. The result is that the mean voltage level of the DC bus will be lower. This can cause to under voltage trip on the VFD.

Register to Reply
Commentator

Join Date: Aug 2006
Posts: 99
Good Answers: 1
#6

Re: 60 Hz VFD on 50 Hz Service

06/06/2012 6:11 AM

THANK YOU ALL FOR THE FEEDBACK. THE vfd MANUFACTURER CONCURS. i LIKE THE REMINDER ABOUT LINE REACTORS; THEY SEEM LIKE A GOOD IDEA ANYWHERE. aS TO THE PUMP PERFORMANCE, MY RELATIONSHIP TO THE AFFINITY LAWS GOES BACK TO THE SLIDE RULE I STILL KEEP IN MY DESK. THE ONE THING I'M SURE OF IS HOW TO SET THE PUMP UP. SOFTWARE MAKES IT A BIT EASIER THESE DAYS.

JT

__________________
Inga Binga Bunga Banga Boonga Binga Buuuunnnnga
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#8
In reply to #6

Re: 60 Hz VFD on 50 Hz Service

06/06/2012 10:02 AM

good to hear that the slide rule is not dead..

__________________
The square root of nothing is what you make it!
Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

askjoet (1); brich (2); JRaef (1); Just an Engineer (1); Rockyscience (1); rudy.leurs (1); SolarEagle (1)

Previous in Forum: Consumption Through Rehostate.   Next in Forum: Motor Insulation Resistance Testing

Advertisement