Motor Insulation Resistance Testing

06/05/2012 2:50 PM

After how much time the insulation resistance of a motor should be checked when not in operation? (I am referring to a motor that is put in service and not to a motor that is in storage. The motor may be not in operation because some other standby motor has been taken in service for example.) The corresponding standard should be stated.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Motor Insulation Resistance Testing

06/05/2012 3:41 PM

Depends on the standard to which the motor was built. Do you know what that was?

What DO you know?

Register to Reply
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#2
In reply to #1

Re: Motor Insulation Resistance Testing

06/05/2012 4:08 PM

IEC motors

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Motor Insulation Resistance Testing

06/05/2012 4:13 PM

Probably

IEC 60034-18-21

Register to Reply
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#4
In reply to #3

Re: Motor Insulation Resistance Testing

06/05/2012 4:35 PM

i do not have a copy of that .so you can please tell me what is in this code regarding my question.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: Motor Insulation Resistance Testing

06/05/2012 7:36 PM

I don't have a copy, either. You should buy one, or ask the motor manufacturer for this information. I don't deal with electric motors any more.

If the motor has always been operated within the specified parameters, then the insulation life should not be a concern until the motor has been in operation for however many hours are specified for its particular insulation class. You can find the class on the nameplate, then maybe you can search for the information yourself, or call the manufacturer.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Motor Insulation Resistance Testing

06/05/2012 8:39 PM

Be realistic lyn, coolyaar buy a publication and read it?

coolyaar if you really need this information you're company would have no problem buying it for you and the company in general.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Aug 2007
Location: Queensland, Australia.
Posts: 159
Good Answers: 4
#7

Re: Motor Insulation Resistance Testing

06/05/2012 11:34 PM

Its a simple test, why not just test it anyway? Is there some limiting factor such as cost, minimal resources, remote location, etc etc. Or, is this for a maintenance plan or something similar?

__________________
Fish dont know they're underwater.......think.
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#8

Re: Motor Insulation Resistance Testing

06/06/2012 3:13 AM

The only reason you should test a motor is if....

1. it has tripped on overload

2. it has blown a fuse

3. been immersed in water

4. subjected to extreme heat

Please feel free to add to this list.....

As for testing a motor "in service".... I see no benefit, and continual testing with a "insulation tester" has been proven to damage the winding insulation.

I have seen motors (and I'm sure others have too) that have been tested, and then fail after 30 seconds, 30 minutes, 30 hours etc.... so if it's gonna blow.... it's gonna blow, and it don't matter what test you do to it!!

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#9

Re: Motor Insulation Resistance Testing

06/06/2012 5:06 AM

It depend on so many factors like- HT or LT motor, insulation class, indoor or outdoor installation, protection type, ambient temp & RH etc.

As of I know, there is no specific standard for it. The reason we need to check is the ingress of moisture & dust along with air inside the winding space and affecting insulation resistance. In rainy season or hot & humid atmosphere it need to be checked more frequently compared to dry and winter weather. So it may range from 10 days to 45 days.

Now a days you can get motors (generally above 15 kW) along with built-in heaters with auto start and shut-off facilities based on timer or temp to protect the insulation resistance. In such motors there is no need to check it.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#10

Re: Motor Insulation Resistance Testing

06/06/2012 7:28 AM

its your choice.

What's your ISO norms stats?

You can test every 6 months / 12 months / 24 months. depend upon the application /environment in which motor is running / any tripping faced etc...

If the motor is placed in Hazardous area, definitely, every time after a gap you start motor, one should check as a safety.

otherwise, no need.

__________________
Exploring the Science of Electricity
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#11
In reply to #10

Re: Motor Insulation Resistance Testing

06/06/2012 7:48 AM

Harry.. the LAST thing you want to do in a hazardous area is introduce a spark potential, as you would/could get from using a 1000v "insulation tester"

Safety first!!

__________________
The square root of nothing is what you make it!
Register to Reply
Power-User

Join Date: Sep 2011
Location: Near the New Madrid Fault. USA
Posts: 269
Good Answers: 1
#13
In reply to #11

Re: Motor Insulation Resistance Testing

06/06/2012 9:25 AM

Yes,, he needs a Baker Surge tester... that will limit the test to just once..

__________________
It's not Rocket Science
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Oct 2011
Posts: 95
#12

Re: Motor Insulation Resistance Testing

06/06/2012 9:03 AM

Mr. Brich,

5. In case of burn smell

6. Observe smoke

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#15
In reply to #12

Re: Motor Insulation Resistance Testing

06/06/2012 5:11 PM

if I found my motor with either one, then I would not waste my time testing!

New motor!!

__________________
The square root of nothing is what you make it!
Register to Reply
Active Contributor

Join Date: Nov 2011
Posts: 13
#14

Re: Motor Insulation Resistance Testing

06/06/2012 3:46 PM

At the time when you want to run it.

Register to Reply
Register to Reply 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

arifkunnath (1); brich (3); claritysable (1); coolyaar (2); harry potter (1); lyn (3); Max Ngwira (1); pritam (1); Rockyscience (1); TonyS (1)

Previous in Forum: 60 Hz VFD on 50 Hz Service   Next in Forum: Generators 200kW No Voltage

Advertisement