Generators 200kW No Voltage

06/06/2012 1:01 AM

hello,

I have stranges things on port diesel generator on a high speed ferry I am working on:

- engine is caterpillar C9

- alternator (200kW) is leroy somer LSA M 46.2L9 C6/4, 400V, 3P, 50Hz, 1500rpm, regul R448 AREP

Nearly each time we start engine, speed is OK but we get no voltage out of the generator, we stop engine and start again and every things is OK. One time, I tried to keep engine running and voltage came after 40seconds running. Sometimes We have to start and stop engine several times before getting voltage.

During normal operation, voltage is stable and diesel generator is working good.

We checked connections and took mesurements of resistance of the windings but found nothing strange.

rem: This Diesel Genetrator is started every 12hours.

rem: The diodes bridges and windings are quite dirty (dust)

We saw 3 technicians about this problem but they have no ideas...

do you have any ideas? do you know any test we can do to find the problem?

thanks again

Register to Reply
Pathfinder Tags: generators
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: generators 200kW no voltage

06/06/2012 1:07 AM

Just from the hip sounds like the exciter circuit is intermittent ......

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#2

Re: generators 200kW no voltage

06/06/2012 6:33 AM

already replied to haulguepa.

problem seems to be with excitor winding insuation. Getting leaky after some fix 100 Hrs. of operation. Cold condition, working OK, Hot running conditions, operation fails.

__________________
Exploring the Science of Electricity
Register to Reply
Associate

Join Date: Jan 2012
Posts: 34
#3

Re: Generators 200kW No Voltage

06/06/2012 4:38 PM

sorry harry,

the problem is not same, it is not the same DG, this one is port side.

The problem of no voltage happen even cold start.

thanks again for your help

pa

Register to Reply
Associate

Join Date: Jan 2012
Posts: 34
#4

Re: Generators 200kW No Voltage

06/07/2012 9:46 PM

no more ideas?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Generators 200kW No Voltage

06/11/2012 3:50 AM

What was the outcome of the telephone call to the original equipment manufacturer's technical helpline?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jan 2012
Posts: 34
#6

Re: Generators 200kW No Voltage

08/17/2012 9:56 PM

still the same problem,

no ideas?

pa

Register to Reply
Associate

Join Date: Jan 2012
Posts: 34
#7

Re: Generators 200kW No Voltage

08/03/2013 4:17 PM

hello,

we finaly changed the AVR and it is ok now.

thanks

pa

Register to Reply