Anonymous Poster #1

Motor 101

06/07/2012 2:54 PM

Regarding 3 phase induction motors.I noticed some of the new motors has multiple voltages on its nameplate.I am not referring to its star delta voltages but for example it says 415v at 50Hz or 380v at 50 Hz.What happen to the equation torque is proportional to voltage squared.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: motor 101

06/07/2012 5:49 PM

The equation has not changed, but governments have tried to interfere with technology. By the way it is the CHANGE in torque is equal to the CHANGE in voltage squared.

Some time ago now, there was a "harmonization" of voltages in Europe and the UK. The UK was using 415V, much of the EU was using 380V, so the "harmonized" voltage became 400V as a compromise. The voltage supply levels in the different countries never actually changed, but equipment mfrs were supposed to all make their motors to be 400V 50Hz, with the understanding that they would be within operating tolerance with both 415V and 380V supplies. That way everything would appear to be "normal". If you have older motors however, they will still say what their original design voltage is. It probably doesn't matter much though.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 3)