06/11/2012 4:04 AM

For single phase ICT 400/220/33 kV 167 MVA the tertiarry arrangement made out side the ICT. the Tertiarry made with Delta formation and use the Lighting Arrestor in this arrangement. My Quation is that How to decide the rating of LA ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Rating of LA

06/11/2012 2:50 PM

Check out the following link, especially the table on page 6. For an ungrounded 33kV system (which is what your delta connection will be), I would expect 36kV or possibly 39kV arresters are needed.

http://www.geindustrial.com/publibrary/checkout/Arresters?TNR=White%20Papers|Arresters|generic

__________________
To get the right answers, first you need to ask the right questions.